Called in a maintenance repair for my InRow air conditioner having a compressor fault and communication errors after a power blip this past weekend (06/11/2016). Guy came in and was replacing parts or something. After a while, he told me that he needed to upgrade the firmware on my units. He started upgrading the first one and 3 hours later the LCD panel still said Download in Process.
The web page says to telnet into the unit for more details. I used telnet to get to the unit and the Device Manager list is empty. FTP shows a bin file for aos and a /sec folder with sshv1k.p15. I don't see a acrp bin file.
He's still on the phone with support. Anything I can do to help him?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:44 PM . Last Modified: 2024-03-18 11:56 PM
Hello. The ACRP bin file will need to load the unit to come up and start running. I have included a link to our FAQ off our website for the three ways of uploading firmware to the units. These units have a Network Management Card (NMC) 1 in them. The only differences is they run on a baud rate of 9600 and if you are serially connecting to them, they use a null modem cable for the cooling units. If he is still having problems please call into our support team.
Thank you
http://www.apc.com/us/en/faqs/index?page=content&id=FA156047
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:44 PM . Last Modified: 2024-03-18 11:56 PM
Hello. The ACRP bin file will need to load the unit to come up and start running. I have included a link to our FAQ off our website for the three ways of uploading firmware to the units. These units have a Network Management Card (NMC) 1 in them. The only differences is they run on a baud rate of 9600 and if you are serially connecting to them, they use a null modem cable for the cooling units. If he is still having problems please call into our support team.
Thank you
http://www.apc.com/us/en/faqs/index?page=content&id=FA156047
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.