Low superheat alarms keep sounding at the site, how to solve it?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-11 01:35 AM
Hello,
First an SR is required to update the unit J5 controller firmware to the latest version and then verify if The evaporator coil outlet temperature sensor is located in a horizontal section of the suction pipe on ACRD30x cooling units. When the compressor is first started, or on units with low load, some liquid refrigerant may be present in this section of pipe, which affects the superheat measurement. Additionally, certain default settings within the display can result in low suction pressure alarms during compressor start-up or during low heat load conditions.
so the SR is required to Relocate the evaporator coil outlet temperature sensor to the vertical section of the suction pipe and adjust various settings in the display
and ensure that there is a sufficient heat loads applied to the unit and verify the gauge readings
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-11 01:35 AM
Hello,
First an SR is required to update the unit J5 controller firmware to the latest version and then verify if The evaporator coil outlet temperature sensor is located in a horizontal section of the suction pipe on ACRD30x cooling units. When the compressor is first started, or on units with low load, some liquid refrigerant may be present in this section of pipe, which affects the superheat measurement. Additionally, certain default settings within the display can result in low suction pressure alarms during compressor start-up or during low heat load conditions.
so the SR is required to Relocate the evaporator coil outlet temperature sensor to the vertical section of the suction pipe and adjust various settings in the display
and ensure that there is a sufficient heat loads applied to the unit and verify the gauge readings
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-11 04:04 AM
Thank you Karim!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of