ACRC103 problem

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ACRC103 problem
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:31 AM . Last Modified: ‎2024-03-18 11:27 PM

0 Likes
1
578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:31 AM . Last Modified: ‎2024-03-18 11:27 PM

ACRC103 problem

Good day. There are 2 installations acrc103 (acrc100 series)  InRow. When power is applied, a cursor appears on the screen and so it is lit permanently, without looking at the menu. I'ts not unresponsive. The system is also unavailable over the network (does not detect the connection). How to restore it?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:31 AM . Last Modified: ‎2024-03-18 11:27 PM

0 Likes
0
578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:31 AM . Last Modified: ‎2024-03-18 11:27 PM

Hello Nikolay. If there is only a blinking cursor on the front screen, this means that the firmware on the Network Management Card (NMC) is not loaded properly. The Firmware will need to be upgraded on the unit. The firmware can be gotten off the website under cooling firmware or off the ACRC103 Product page. I have included a link below for the upgrading procedures on the NMC. If this link does not work go to APC.com and under Support go to FAQ's and search for "How do I Upgrade the firmware on an APC Network Management Card (NMC) or NMC embedded device (Rack PDU, ect). This document has the steps to upgrade the firmware. The ACRC103 has an NMC 1 in it. There are two small changes from the document for these units. First they use a NULL Modem cable for the serial connection if you need to connect serially. Second, if connecting serially the baud rate is 9600 for these units (not the 2400 in the document).

Thank you

https://www.apc.com/us/en/faqs/index?page=content&id=FA156047&actp=search&viewlocale=en_US&searchid=...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:31 AM . Last Modified: ‎2024-03-18 11:27 PM

0 Likes
0
579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:31 AM . Last Modified: ‎2024-03-18 11:27 PM

Hello Nikolay. If there is only a blinking cursor on the front screen, this means that the firmware on the Network Management Card (NMC) is not loaded properly. The Firmware will need to be upgraded on the unit. The firmware can be gotten off the website under cooling firmware or off the ACRC103 Product page. I have included a link below for the upgrading procedures on the NMC. If this link does not work go to APC.com and under Support go to FAQ's and search for "How do I Upgrade the firmware on an APC Network Management Card (NMC) or NMC embedded device (Rack PDU, ect). This document has the steps to upgrade the firmware. The ACRC103 has an NMC 1 in it. There are two small changes from the document for these units. First they use a NULL Modem cable for the serial connection if you need to connect serially. Second, if connecting serially the baud rate is 9600 for these units (not the 2400 in the document).

Thank you

https://www.apc.com/us/en/faqs/index?page=content&id=FA156047&actp=search&viewlocale=en_US&searchid=...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of