ACRC103 Warmstart and Cold Starts

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ACRC103 Warmstart and Cold Starts
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:40 PM . Last Modified: ‎2024-03-19 12:01 AM

0 Likes
1
711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:40 PM . Last Modified: ‎2024-03-19 12:01 AM

ACRC103 Warmstart and Cold Starts

We have a couple of ACRC103 Inrows and we are periodically getting Warmstarts and Cold Starts.

07.04.2016 09:02:47 InRow RC: Controller Reset - Cold Start because of a unknown reason.
07.04.2016 09:02:47 InRow RC: Internal communication established.
07.04.2016 09:02:36 System: Network service started. System IP is xxx.xxx.xxx.xxx from manually configured settings.
07.04.2016 09:02:36 System: Warmstart.
07.04.2016 08:02:18 InRow RC: Controller Reset - Cold Start because of a unknown reason.
07.04.2016 08:02:18 InRow RC: Internal communication established.
07.04.2016 08:02:08 System: Network service started. System IP is xxx.xxx.xxx.xxx from manually configured settings.
07.04.2016 08:02:08 System: Warmstart.

Anyone know what is causing this?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:40 PM . Last Modified: ‎2024-03-19 12:01 AM

0 Likes
0
710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:40 PM . Last Modified: ‎2024-03-19 12:01 AM

Hello Craig. I have copied in a link to our Knowledge base that goes in-depth on the warmstarts and what causes them. It basically comes down to the network card lost communication with the network, so it will reboot itself to try and regain connection. Please let me know if you need anything else.

Thank you

http://www.apc.com/site/support/us/en/faq/

search for

Why does my Network Management Card report warmstarts/coldstarts or network interface restarts/coldstarts?

Cause


A System Coldstart event indicates that the NMC (Network Management Card) has just been powered and has completed startup.

  • Power interruption to the NMC - If a device powering the NMC suffers an interruption of power, the NMC will restart when power is reapplied to that device.

A System Warmstart (or restart) event indicates that the NMC has rebooted and completed startup, without losing power. This may be due to any of the conditions mentioned below.
  • The default gateway is wrong or the network traffic is too heavy and the gateway can not be reached.
The default gateway can be any valid node's IP on the network management card's network. The Management Card implements internal watchdog mechanisms to protect itself from becoming inaccessible over the network. For example, if the Management Card does not receive any network traffic for 9.5 minutes (either direct traffic, such as SNMP,or broadcast traffic, such as an Address Resolution Protocol [ARP] request), it assumes that there is a problem with its network interface and restarts to prevent further problems. To ensure that the Management Card does not restart if the network is quiet for 9.5 minutes, the Management Card attempts to contact the default gateway every 4.5 minutes. If the gateway is present, it responds to the Management Card, and that response restarts the 9.5-minute timer. If your application does not require or have a gateway, specify the IP address of a computer that is running on the network most of the time and is on the same subnet. The network traffic of that computer will restart the 9.5-minute timer frequently enough to prevent the Management Card from restarting.  
  • FTP upload completion - After a new AOS or Application firmware upgrade has been uploaded to the NMC the NMC will automatically reboot and run the new firmware.
  • Logout if settings are changed - Modification of some NMC settings will require a reboot of the NMC.
  • Reset Switch - If the Reset button on the front panel of the NMC is pressed the NMC will reboot immediately.
  • Web Interface Reboot request - One of the NMC options for Reboot was selected in the Web User Interface.
  • Network settings have changed - At least one of the TCP/IP settings changed. The system will need to reboot for the settings to take effect.
  • Restart SNMP Agent (SNMP v1 or v3) - A request to restart the current SNMP agent service was received. Majority of SNMP configuration changes will require an SNMP agent service restart to apply the change.
  • Load and Execute SNMP Agent Service (SNMP v1 or v3) - An internal request to load and execute a new SNMP agent service was received. Enabling or disabling SNMP v1 or v3 will require a restart to apply the change.
  • Clear Network and Start SNMP Agent (SNMP v1 or v3) - A request to clear the NMC's network settings and restart the SNMP agent service was received.
  • Smart-UPS Output Voltage Change - Some Smart-UPS models allow the output voltage to be changed. This requires a reboot of the NMC firmware.
     
  • Remote Monitoring Service (RMS) communication has been lost (NMC2 only) - If for a certain period of time, RMS communication is lost, you may see several System: RMS failed to communicate with the server events followed by a Warmstart/Network Interface Restart message in the NMC2 event log. This is normal and the NMC2 reboots in this situation as a failsafe mechanism in case the communication problem is internal to the NMC2.On NMC2, it may be helpful to obtain the debug.txt or dump.txt file from the card's file system in the /dbg folder to help validate, if the files are present.
  • Detected Firmware Error - An internal firmware error was detected by the NMC and to clear the error, the NMC firmware explicitly reboots itself as a failsafe. On NMC2, it may be helpful to obtain the debug.txt or dump.txt file from the card's file system in the /dbg folder to help validate, if the files are present.
  • Unrecoverable Firmware Error - An undetected firmware error occurred and the hardware watchdog reboots the NMC to clear the error. On NMC2, it may be helpful to obtain the debug.txt or dump.txt file from the card's file system in the /dbg folder to help validate, if the files are present.

 
Resolution

 

It is recommended to follow the instructions in article FA156131 and download all available event logs for your product. This includes event.txt, data.txt, and config.ini for NMC1 and NMC2 as well as debug.txt and dump.txt for NMC2 only.



For NMC1:
 

  • Review the event.txt file to see if any of the causes listed above could be why your Network Management Card has restarted or coldstarted.
  • Is this affecting more than one Network Management Card in your environment? This may point to a network traffic issue (too much, to little, or "bad" packets)  causing the Management Card to reboot due to the watchdog mechanism outlined above.
  • Note the frequency of the events in question. Can you pinpoint it to a certain time/certain set of events before and after?
    • If the warmstarts/network interface restarts are always the same amount of time apart, this may relate to a network traffic issue as well.
  • Depending on what you find, try rebooting your card's interface or resetting the card to defaults (after backing up your configuration). See if the issue persists.
  • Please contact APC support at any time for additional options and help to obtain a root cause for a warmstart/restart/coldstart. Also note these types of events don't always necessarily indicate a problem and only affect the Network Management Card's interface. Your UPS or device load is unaffected. Please have your log files (event.txt, data.txt, config.ini) available for tech support to review.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:40 PM . Last Modified: ‎2024-03-19 12:01 AM

0 Likes
0
711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:40 PM . Last Modified: ‎2024-03-19 12:01 AM

Hello Craig. I have copied in a link to our Knowledge base that goes in-depth on the warmstarts and what causes them. It basically comes down to the network card lost communication with the network, so it will reboot itself to try and regain connection. Please let me know if you need anything else.

Thank you

http://www.apc.com/site/support/us/en/faq/

search for

Why does my Network Management Card report warmstarts/coldstarts or network interface restarts/coldstarts?

Cause


A System Coldstart event indicates that the NMC (Network Management Card) has just been powered and has completed startup.

  • Power interruption to the NMC - If a device powering the NMC suffers an interruption of power, the NMC will restart when power is reapplied to that device.

A System Warmstart (or restart) event indicates that the NMC has rebooted and completed startup, without losing power. This may be due to any of the conditions mentioned below.
  • The default gateway is wrong or the network traffic is too heavy and the gateway can not be reached.
The default gateway can be any valid node's IP on the network management card's network. The Management Card implements internal watchdog mechanisms to protect itself from becoming inaccessible over the network. For example, if the Management Card does not receive any network traffic for 9.5 minutes (either direct traffic, such as SNMP,or broadcast traffic, such as an Address Resolution Protocol [ARP] request), it assumes that there is a problem with its network interface and restarts to prevent further problems. To ensure that the Management Card does not restart if the network is quiet for 9.5 minutes, the Management Card attempts to contact the default gateway every 4.5 minutes. If the gateway is present, it responds to the Management Card, and that response restarts the 9.5-minute timer. If your application does not require or have a gateway, specify the IP address of a computer that is running on the network most of the time and is on the same subnet. The network traffic of that computer will restart the 9.5-minute timer frequently enough to prevent the Management Card from restarting.  
  • FTP upload completion - After a new AOS or Application firmware upgrade has been uploaded to the NMC the NMC will automatically reboot and run the new firmware.
  • Logout if settings are changed - Modification of some NMC settings will require a reboot of the NMC.
  • Reset Switch - If the Reset button on the front panel of the NMC is pressed the NMC will reboot immediately.
  • Web Interface Reboot request - One of the NMC options for Reboot was selected in the Web User Interface.
  • Network settings have changed - At least one of the TCP/IP settings changed. The system will need to reboot for the settings to take effect.
  • Restart SNMP Agent (SNMP v1 or v3) - A request to restart the current SNMP agent service was received. Majority of SNMP configuration changes will require an SNMP agent service restart to apply the change.
  • Load and Execute SNMP Agent Service (SNMP v1 or v3) - An internal request to load and execute a new SNMP agent service was received. Enabling or disabling SNMP v1 or v3 will require a restart to apply the change.
  • Clear Network and Start SNMP Agent (SNMP v1 or v3) - A request to clear the NMC's network settings and restart the SNMP agent service was received.
  • Smart-UPS Output Voltage Change - Some Smart-UPS models allow the output voltage to be changed. This requires a reboot of the NMC firmware.
     
  • Remote Monitoring Service (RMS) communication has been lost (NMC2 only) - If for a certain period of time, RMS communication is lost, you may see several System: RMS failed to communicate with the server events followed by a Warmstart/Network Interface Restart message in the NMC2 event log. This is normal and the NMC2 reboots in this situation as a failsafe mechanism in case the communication problem is internal to the NMC2.On NMC2, it may be helpful to obtain the debug.txt or dump.txt file from the card's file system in the /dbg folder to help validate, if the files are present.
  • Detected Firmware Error - An internal firmware error was detected by the NMC and to clear the error, the NMC firmware explicitly reboots itself as a failsafe. On NMC2, it may be helpful to obtain the debug.txt or dump.txt file from the card's file system in the /dbg folder to help validate, if the files are present.
  • Unrecoverable Firmware Error - An undetected firmware error occurred and the hardware watchdog reboots the NMC to clear the error. On NMC2, it may be helpful to obtain the debug.txt or dump.txt file from the card's file system in the /dbg folder to help validate, if the files are present.

 
Resolution

 

It is recommended to follow the instructions in article FA156131 and download all available event logs for your product. This includes event.txt, data.txt, and config.ini for NMC1 and NMC2 as well as debug.txt and dump.txt for NMC2 only.



For NMC1:
 

  • Review the event.txt file to see if any of the causes listed above could be why your Network Management Card has restarted or coldstarted.
  • Is this affecting more than one Network Management Card in your environment? This may point to a network traffic issue (too much, to little, or "bad" packets)  causing the Management Card to reboot due to the watchdog mechanism outlined above.
  • Note the frequency of the events in question. Can you pinpoint it to a certain time/certain set of events before and after?
    • If the warmstarts/network interface restarts are always the same amount of time apart, this may relate to a network traffic issue as well.
  • Depending on what you find, try rebooting your card's interface or resetting the card to defaults (after backing up your configuration). See if the issue persists.
  • Please contact APC support at any time for additional options and help to obtain a root cause for a warmstart/restart/coldstart. Also note these types of events don't always necessarily indicate a problem and only affect the Network Management Card's interface. Your UPS or device load is unaffected. Please have your log files (event.txt, data.txt, config.ini) available for tech support to review.
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of