240v to 208v conversion in Symmetra UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 240v to 208v conversion in Symmetra UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:55 AM . Last Modified: ‎2024-03-07 11:46 PM

0 Likes
4
3167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:55 AM . Last Modified: ‎2024-03-07 11:46 PM

240v to 208v conversion in Symmetra UPS

Can someone explain how the Symmetra LX 16kVA converts 240v power to 208v power? I install SmartHomes and would like to use this UPS as it is a great size for the typical home installation. Does the UPS use transformers to stepdown the power? Home installations usually have 240v but the equipment I use operates more efficiently at 208, another reason this UPS would be perfect for this application.

Please help.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:55 AM . Last Modified: ‎2024-03-07 11:46 PM

0 Likes
0
3164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:55 AM . Last Modified: ‎2024-03-07 11:46 PM

I believe what you are looking for is the reason that you can output 208v even with an input of 240v. In order to explain this, you need to understand the difference between 208 and 240. Both are derived by referencing (2) 120v hot legs to eachother, only difference being the "phase angle" between the 2 legs.

The Symmetra LX UPS system actually has the ability to alter the phase angle on the output side of the UPS. KVAR is correct - the UPS recreates the waveform to produce output power, however, with the ability to change the phase angle between the 2 phases (or hot legs) we can output 208v, even with 240v input (or vice versa).

In bypass, the UPS passes the voltage through, without the ability to change the phase angle, therefore outputting what is input to the UPS. This would be the only concern for your installation. If the UPS is in bypass, you will output 240v in bypass rather than 208v.

Generally, APC recommends matching the output with the input for this very reason, however, it is always an option to output one voltage or the other regardless of the input voltage.

Shoot me a personal message if you need me to clarify any of this for you, I tried to keep it simple for you.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:55 AM . Last Modified: ‎2024-03-07 11:46 PM

0 Likes
0
3164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:55 AM . Last Modified: ‎2024-03-07 11:46 PM

It's a double conversion UPS.
Input voltage is turned into DC, then the output power is completely regenerated with an inverter.
See page 6
http://www.apcmedia.com/salestools/SADE-5TNM3Y_R5_EN.pdf

In bypass mode, it is likely using transformers.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:55 AM . Last Modified: ‎2024-03-07 11:46 PM

0 Likes
0
3165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:55 AM . Last Modified: ‎2024-03-07 11:46 PM

I believe what you are looking for is the reason that you can output 208v even with an input of 240v. In order to explain this, you need to understand the difference between 208 and 240. Both are derived by referencing (2) 120v hot legs to eachother, only difference being the "phase angle" between the 2 legs.

The Symmetra LX UPS system actually has the ability to alter the phase angle on the output side of the UPS. KVAR is correct - the UPS recreates the waveform to produce output power, however, with the ability to change the phase angle between the 2 phases (or hot legs) we can output 208v, even with 240v input (or vice versa).

In bypass, the UPS passes the voltage through, without the ability to change the phase angle, therefore outputting what is input to the UPS. This would be the only concern for your installation. If the UPS is in bypass, you will output 240v in bypass rather than 208v.

Generally, APC recommends matching the output with the input for this very reason, however, it is always an option to output one voltage or the other regardless of the input voltage.

Shoot me a personal message if you need me to clarify any of this for you, I tried to keep it simple for you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:56 AM . Last Modified: ‎2024-03-07 11:45 PM

0 Likes
0
3164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:56 AM . Last Modified: ‎2024-03-07 11:45 PM

The inverter generates two phases separated by 120° yielding 120v and 208v(120 * sqrt 3) in 208/120 mode and separated by 180° in 120/240 mode.

The former duplicates two of the three phases found in 208Y/120v service found in commercial buildings but your house current is usually out of phase by 180° yielding 120 & 240.


N+1, what's the no load power consumption and what's the efficiency in ~1-2kW output range likely to be seen in home use?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:56 AM . Last Modified: ‎2024-03-07 11:45 PM

0 Likes
0
3164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:56 AM . Last Modified: ‎2024-03-07 11:45 PM

Thanks KVAR,

Im trying to remember back to College power classes, it has been awhile. The load on this UPS would likely be approx 6000-8000 watts, and will be powered from a separate 100amp feed to the house. We install several large servers that store most of the home's configuration tools, networking gear, one small 120v circuit (20amps max) that is powered even when the power is out (for alarm clocks and such around the house). This customer specifically also requires a home office and small business tools (a few servers and other networking gear). Its quite a complicated setup, but very fun to configure, especially when there is no maximum budget.

Thanks for your detailed explanation again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore