16A or 32A connector
Hi, I am puchasing an APC Smart UPS 3000VA SURTD3000RMXLI and I am putting the power supply in the room. Do I need a 16A or 32A connector for this? I think a 32A but can anyone confirm that?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-1204:41 AM. Last Modified: 2024-01-3102:58 AM
Hello,
Everything I see shows this UPS has a C20 input which for 230V operation would require 16A branch circuit breaker, not 32A. The 5000VA uses/requires a 32A.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-1204:41 AM. Last Modified: 2024-01-3102:58 AM
Hello,
Everything I see shows this UPS has a C20 input which for 230V operation would require 16A branch circuit breaker, not 32A. The 5000VA uses/requires a 32A.