Hi, I am puchasing an APC Smart UPS 3000VA SURTD3000RMXLI and I am putting the power supply in the room. Do I need a 16A or 32A connector for this? I think a 32A but can anyone confirm that?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-12 04:41 AM . Last Modified: 2024-01-31 02:58 AM
Hello,
Everything I see shows this UPS has a C20 input which for 230V operation would require 16A branch circuit breaker, not 32A. The 5000VA uses/requires a 32A.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-12 04:41 AM . Last Modified: 2024-01-31 02:58 AM
Hello,
Everything I see shows this UPS has a C20 input which for 230V operation would require 16A branch circuit breaker, not 32A. The 5000VA uses/requires a 32A.