Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82125members
349633posts

Smart-UPS 3000 - Auto shutdown after power loss.

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Choakem
Crewman
Crewman
0 Likes
2
252

Smart-UPS 3000 - Auto shutdown after power loss.

Hello All,

 

Is it possible to configure the Smart-UPS 3000 to power off after X time if there's a power outage?

 

I've tried going through the menu but cannot achieve power off in the event of a power outage.

 

ANY advice would be greatly appreciated.

 

Michael.

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
1
239

Re: Smart-UPS 3000 - Auto shutdown after power loss.

@Choakem 

 

If the UPS is an SMT, SMX, or SRT Smart-UPS, you can configure the UPS to shut down when on battery. From the LCD panel, go to Configuration and change the type to Advanced. Then scroll down, and you can configure load shedding.

The menu options are provided in the UPS user's guide.

 

Tags (1)
Choakem
Crewman
Crewman
0 Likes
0
233

Re: Smart-UPS 3000 - Auto shutdown after power loss.

Thanks Bob, 

I'll be onsite tomorrow.


It's a SMT3000IC model.

 

I've never seen that option in advanced settings!!

 

I know I dont have any network card other than the cloud monitoring one.....

 

Ill take a look for "load shedding" and report back 😛

 

Thank-you!

Tags (1)