How to set up Network Shutdown on Linux host with VMware Workstation?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to set up Network Shutdown on Linux host with VMware Workstation?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
sigi_apc
Crewman sigi_apc
Crewman

Posted: ‎2021-06-29 05:34 AM . Last Modified: ‎2024-03-13 12:52 AM

0 Likes
1
1795
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:34 AM . Last Modified: ‎2024-03-13 12:52 AM

How to set up Network Shutdown on Linux host with VMware Workstation?

I have a Linux host (Ubuntu Desktop) which runs VMware Workstation to host some virtual machines. Now I'd like to use PowerChute Network Shutdown to shut down the Linux host in case of power failure.

My idea was to simply install PowerChute Network Shutdown on the Linux host and use a pre-shutdown command to stop the VMs before (vmrun).

When trying to install PowerChute Network Shutdown 4.2 for Linux x64 on my Linux machine I get the error message that installation is not supported since VMware is running on the same machine. Well, that is not what I was expecting...

Reading the PowerChute Installation Guide none of the VMware option fits to my setup. I neither have an additional Windows machine to monitor the VMware Host nor a I'd like to run the PowerChute Virtual Appliance in VMware Workstation. I am even not sure if the latter is supported, the PowerChute User Guide for VMware does not mention VMware Workstation.

Any suggestions how to set up Network Shutdown in my scenario?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • vmware
  • workstation
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sigi_apc
Crewman sigi_apc
Crewman

Posted: ‎2021-06-29 05:34 AM . Last Modified: ‎2024-03-13 12:51 AM

0 Likes
0
1791
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:34 AM . Last Modified: ‎2024-03-13 12:51 AM

Hi, this is for those who are interested in a solution for this scenario.

I've contacted APC support and asked the same question. Their proposal was to try an older PCNS version.

So I downloaded PCNS 3.1.0 for Linux from here: ftp://ftp.apc.com/restricted/software/pcns/310/

Note: You have to provide username and password with the URL (ftp://:@ftp.apc.com/restricted/software/pcns/310) where is "restrict" and is... Well I don't want to post it here. You can find it out by starting a regular PCNS download and looking into the link address of the final download button.

The PCNS 3.1.0 installed successfully on Ubuntu 14.04.5 without complaining that VMware Workstation is installed. Obviously there is not really an incompatibility between PCNS 3.1.0 and VMware Workstation 10.0.6, both work fine after the PCNS installation.

PCNS triggered shutdown works as expected. Configuring a shell script as shutdown command which calls "vmrun stop soft" properly shuts down the VMs before Linux is going down for halt. smile

Maybe a wish to the PCNS development team: If there also no real incompatibility between PCNS 4.2 and VMware Workstation you might refine the check for VMware and allow installation of PCNS 4.2 in this scenario. I'd appreciate if I could upgrade PCNS to 4.2... Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Reply 1
sigi_apc
Crewman sigi_apc
Crewman

Posted: ‎2021-06-29 05:34 AM . Last Modified: ‎2024-03-13 12:51 AM

0 Likes
0
1792
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:34 AM . Last Modified: ‎2024-03-13 12:51 AM

Hi, this is for those who are interested in a solution for this scenario.

I've contacted APC support and asked the same question. Their proposal was to try an older PCNS version.

So I downloaded PCNS 3.1.0 for Linux from here: ftp://ftp.apc.com/restricted/software/pcns/310/

Note: You have to provide username and password with the URL (ftp://:@ftp.apc.com/restricted/software/pcns/310) where is "restrict" and is... Well I don't want to post it here. You can find it out by starting a regular PCNS download and looking into the link address of the final download button.

The PCNS 3.1.0 installed successfully on Ubuntu 14.04.5 without complaining that VMware Workstation is installed. Obviously there is not really an incompatibility between PCNS 3.1.0 and VMware Workstation 10.0.6, both work fine after the PCNS installation.

PCNS triggered shutdown works as expected. Configuring a shell script as shutdown command which calls "vmrun stop soft" properly shuts down the VMs before Linux is going down for halt. smile

Maybe a wish to the PCNS development team: If there also no real incompatibility between PCNS 4.2 and VMware Workstation you might refine the check for VMware and allow installation of PCNS 4.2 in this scenario. I'd appreciate if I could upgrade PCNS to 4.2... Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now