Do I need to turn OFF the UPS after I shut down the computer

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Do I need to turn OFF the UPS after I shut down the computer
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
134
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:59 AM

0 Likes
10
44581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:59 AM

Do I need to turn OFF the UPS after I shut down the computer

Hi,

I just got my Smart-UPS, Model: SMT750I, and have connected my computer and monitor on it. Now I have a very simple question:

Do i need to turn OFF the UPS, after I shut down my computer or not?

If yes, how? Via power button on the UPS...? Or do i need some software for computer? And how do I connect my PC and UPS: via USB, or UPS Monitoring port?

Thank you in advance

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

I agree it is not a bad idea during storms or similar..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44580
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

Hi Dario,

The answer to your question would depend on certain conditions. If you have just turned off your PC because you are done with your work and there is no power problem you can turn the UPS via the power button. As long as there is input power coming in to your UPS, it will charge the battery.

With regards to connecting your UPS to your computer for monitoring purposes you can connect both the USB or Serial/UPS Monitoring Port can do the job. You can also purchase a network management card if you do need to have network manageability of the UPS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

1 Like
1
44581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

i would say it is not a requirement to turn the UPS off every single time you turn your computer off. the UPS is designed to be left on all of the time and I don't see a benefit to turn it off each day. also, every time you turn the UPS on, it will do a UPS self test and if done too often, this will drain the battery a tiny bit unnecessarily. if you do this a few times a day for a year, then it adds up.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

I agree.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

I just dug up this thread while researching this issue. I have back ups es 500. I was wondering if it would be better for me to press the APC power button after done using. Typically 1-3 times daily. Hooked up to my battery back up APC ports is my plasma TV, ps3 and PC. None of these device require constant power when not in use. How much electricity is being used/saved when power button on APC is turned off. Is the APC really charging at the same rate whether or not the power button on APC is pressed? I don't know if it matters but I never bothered networking my APC or installing software.

Message was edited by: leif2

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

andreiguird_apc
Crewman andreiguird_apc
Crewman

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

Just want to get clarification, which is the best practice for the UPS after computer is shut down?

1) Turn off the UPS but let the UPS still plugged to main outlet (keep charging the battery)

2) Turn off the UPS and also disconnect it from main outlet (the battery would discharge slowly in this state)

3) Let the UPS keep turned on.

I have tried the 1st one, the UPS will keep getting warm while it's turned off. Would this affect longevity of the components inside?

For the 3rd one, if I'm not in home and there is blackout, the UPS will turn into battery mode and the battery will keep discharging until it's run out. If it often happens, would this reduce the battery life greatly compared to 2nd method ?

UPDATE:

it's been answered here, the first method is the best one.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

I agree it is not a bad idea during storms or similar..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

Hi,

I just got my Smart-UPS, Model: SMT750I, and have connected my computer and monitor on it. Now I have a very simple question:

Do i need to turn OFF the UPS, after I shut down my computer or not?

If yes, how? Via power button on the UPS...? Or do i need some software for computer? And how do I connect my PC and UPS: via USB, or UPS Monitoring port?

Thank you in advance

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

Hi Dario,

The answer to your question would depend on certain conditions. If you have just turned off your PC because you are done with your work and there is no power problem you can turn the UPS via the power button. As long as there is input power coming in to your UPS, it will charge the battery.

With regards to connecting your UPS to your computer for monitoring purposes you can connect both the USB or Serial/UPS Monitoring Port can do the job. You can also purchase a network management card if you do need to have network manageability of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

1 Like
1
44582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

i would say it is not a requirement to turn the UPS off every single time you turn your computer off. the UPS is designed to be left on all of the time and I don't see a benefit to turn it off each day. also, every time you turn the UPS on, it will do a UPS self test and if done too often, this will drain the battery a tiny bit unnecessarily. if you do this a few times a day for a year, then it adds up.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

I agree.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

I just dug up this thread while researching this issue. I have back ups es 500. I was wondering if it would be better for me to press the APC power button after done using. Typically 1-3 times daily. Hooked up to my battery back up APC ports is my plasma TV, ps3 and PC. None of these device require constant power when not in use. How much electricity is being used/saved when power button on APC is turned off. Is the APC really charging at the same rate whether or not the power button on APC is pressed? I don't know if it matters but I never bothered networking my APC or installing software.

Message was edited by: leif2

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

no, honestly a UPS is intended to be on all the time by design. i see no benefit of turning it on or off daily. just turn it on and leave it on.

Reply

Link copied. Please paste this link to share this article on your social media post.

andreiguird_apc
Crewman andreiguird_apc
Crewman

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

0 Likes
0
44582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:34 AM . Last Modified: ‎2024-03-11 12:58 AM

Just want to get clarification, which is the best practice for the UPS after computer is shut down?

1) Turn off the UPS but let the UPS still plugged to main outlet (keep charging the battery)

2) Turn off the UPS and also disconnect it from main outlet (the battery would discharge slowly in this state)

3) Let the UPS keep turned on.

I have tried the 1st one, the UPS will keep getting warm while it's turned off. Would this affect longevity of the components inside?

For the 3rd one, if I'm not in home and there is blackout, the UPS will turn into battery mode and the battery will keep discharging until it's run out. If it often happens, would this reduce the battery life greatly compared to 2nd method ?

UPDATE:

it's been answered here, the first method is the best one.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

gohook
gohook
Cadet

Posted: ‎2024-07-20 05:42 PM

In response to BillP
0 Likes
0
14279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-20 05:42 PM

So the ANZWER is :  YOU DO NOT NEED TO TURN OFF THE  APS UPS PoWER SAFETY SUPPLAY WHEN TURN OFF THE DESKTOP COMPUTER & 24 Inch SCREEN.

 

Let it be ON.   

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

MorneMeintjes
Ensign MorneMeintjes
Ensign

Posted: ‎2024-07-22 11:42 PM

0 Likes
0
14179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-22 11:42 PM

Good morning.

It all depends why you are switching off. If its to give the UPS longevity its better to leave the UPS on.

The UPS needs to keep its batteries charged. Charged batteries have a longer life span. If you switch off your UPS for more than a week or two its better to disconnect the batteries. However if the batteries are not charged at least every three months, they will discharge, and due to sulfation your backup time will be reduced. Very long periods with out charging the battery will eventually lead to battery death. 

Just leave the UPS on, to charge its batteries. Also the battery takes a long time to charge, it keeps charging even after the UPS indicates the battery was replenished.

Its better to leave your UPS ON. In storms it may be a good idea to switch off.

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore