Posted: 2021-06-28 05:16 AM
This was originally posted on APC forums on 5/12/2010
Hi,
So i have a AP9225 with an ap9617 management card. I upgraded the firmware on it to 3.7.3 but i put the firmware for a UPS on it. I need to find a way to put the correct firmware back on. I have looked through the forum and downloaded this firmware ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/security/v258b/ but i am unable to get the new firmware on using FTP.
Thanks
Posted: 2021-06-28 05:17 AM
This was originally posted on APC forums on 5/12/2010
Hi,
So i have a AP9225 with an ap9617 management card. I upgraded the firmware on it to 3.7.3 but i put the firmware for a UPS on it. I need to find a way to put the correct firmware back on. I have looked through the forum and downloaded this firmware ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/security/v258b/ but i am unable to get the new firmware on using FTP.
Thanks
Posted: 2021-06-28 05:16 AM
This reply was originally posted by Angela on APC forums on 8/19/2014
Hello - I'd have to spend sometime reviewing those old release notes but I would likely upgrade, especially if it is like version 1. My notes list what you have there as the latest version.
AP9225 - MSPlus - AP9606 or AP9617
AP9606
AOS: aos254.bin
APP: msp200.bin
AP9617
apc_hw02_aos_264.bin
apc_hw02_msp_262.bin
Posted: 2021-06-28 05:16 AM
This was originally posted on APC forums on 8/20/2014
Thanks Angela, so if I run this file "apc_hw02_aos264_msp262.exe" will that also update the firmware on both 9225's or just the 9617?
Thanks again
Posted: 2021-06-28 05:16 AM
This reply was originally posted by Angela on APC forums on 8/20/2014
Hi again - it would just apply it to the IP address of the AP9617 in the main unit. I don't think these support the capability to update each other. I don't know too much about that expansion unit really - does it have its own network interface or just a connection to the main unit?
Posted: 2021-06-28 05:16 AM
This reply was originally posted by Angela on APC forums on 8/21/2014
You just need to follow the NMC1 (AP9617/18/19) instructions here -> How do I upgrade the firmware on an APC Network Management Card? | FAQs | US
Posted: 2021-06-28 05:16 AM
This was originally posted on APC forums on 8/21/2014
Great thanks again!
Posted: 2021-06-28 05:17 AM
This was originally posted on APC forums on 5/12/2010
Thanks, Everthing is working now.
Posted: 2021-06-28 05:17 AM
This reply was originally posted by Angela on APC forums on 5/12/2010
no problem
Posted: 2021-06-28 05:17 AM
This was originally posted on APC forums on 8/21/2014
Angela, there is no network interface on the 9225EXP, so I assume this would need to be done via xmodem. For the 9225 firmware...how do you update it?
Posted: 2021-06-28 05:17 AM
This was originally posted on APC forums on 5/12/2010
Hi,
So i have a AP9225 with an ap9617 management card. I upgraded the firmware on it to 3.7.3 but i put the firmware for a UPS on it. I need to find a way to put the correct firmware back on. I have looked through the forum and downloaded this firmware ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/security/v258b/ but i am unable to get the new firmware on using FTP.
Thanks