Troubleshooting why Capture Index values do not display
The cooling simulation updates based on the equipment placement. If your configuration is invalid, the tool tip will inform you of the problem.
If the cooling calculations do not run, verify your configuration is not invalid due to one of the following:
- The distance between the racks is insufficient (at least 2 feet). Hot air blows from one rack into the front of another rack.
To make the cooling configuration valid, use the room layout icons and drag the row border to make the aisle wider.
- The row layout is not well designed.
- The equipment is placed in pairs directly across from each other but is misaligned by 10 cm or more.
To make the cooling configuration valid, drag the equipment closer to each other.
- There is a piece of equipment placed in the aisle between the rows.
To make the cooling configuration valid, move the equipment out of the aisle.