Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
About Capture Index prediction models
Working with the Capture Index
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Unlike temperature-based metrics, Capture Index (CI) is solely a function of airflow. There are two kinds of CI:
Cold Aisle CI: the fraction of air ingested by the rack which originates from local cooling resources (e.g. perforated floor tiles or local coolers)
Hot Aisle CI: the fraction of air exhausted by a rack which is captured by local extracts (e.g. local coolers or return vents)
CI measures effectiveness of supplying cooling air to rack inlets or scavenging heated air from rack exhausts on a 0% (bad) to 100% (good) scale.
CI is defined in terms of local cooling resources (airflow from tiles, local coolers, local extract vents, etc.) and it measures the robustness and scalability of a grouping of equipment.
Example
Cold Aisle The Cold Aisle Capture Index of the top-middle rack is 84%. In other words, 84% of the airflow drawn in by that rack originated from the perforated floor tiles. The remaining 16% of inlet air comes from other sources including the room ambient and recirculation from the subject rack and others.
Hot Aisle The Hot Aisle Capture Index of the bottom-right rack is 66%. In other words, 66% of the exhaust airflow from this rack is captured by the local coolers while the additional 34% escapes, heating the room ambient and, potentially, entering rack inlets.