Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Troubleshooting issues connecting your Gateway to EcoStruxure IT

Troubleshooting

How to troubleshoot and solve issues configuring the EcoStruxure IT Gateway

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Gateway
  • Troubleshooting
  • Troubleshooting issues connecting your Gateway to EcoStruxure IT
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Gateway configuration file edit required after inc...
  • How to troubleshoot the Gateway connection to EcoS...
  • How to troubleshoot SNMP communication issues in t...
  • How to solve the cloud connectivity untrusted SSL ...
  • How to set up the Gateway proxy settings
  • How to restart the Gateway Service
  • How to replace the self-signed SSL certificate in ...
  • How to replace a device in EcoStruxure IT Gateway
  • How to disconnect or reconnect a Gateway from EcoS...
  • How to create a device walk file for EcoStruxure I...
  • How to allow a targeted read for Device Support
  • Gathering Gateway logs for troubleshooting
  • Gateway restore fails on some non-English locales
  • Gateway appliance network problems due to bad imag...
  • Gateway Device Communication Alert
  • Galaxy UPS is offline after updating the Gateway
  • Device serial numbers and unique identifiers
  • Device is offline after replacement or RMA
  • Device discover fails - SNMP is disabled by defaul...
  • Cannot discover Redfish devices in Gateway
  • Cannot discover NetBotz devices in Gateway
  • Web server port 443 is being used by another appli...
  • Troubleshooting issues connecting your Gateway to ...
  • Troubleshooting Gateway device discovery failure
  • SNMP walks, Modbus polls, and Redfish discoveries
  • NetBotz devices appear in the list of unknown devi...
  • NetBotz 4.x discovery issue when Gateway proxy set...
  • My device name didn't update in the Gateway after ...
  • My device is not responding - Gateway 1.4.0
  • Gateway configuration file edit required after inc...
  • How to troubleshoot the Gateway connection to EcoS...
  • How to troubleshoot SNMP communication issues in t...
  • How to solve the cloud connectivity untrusted SSL ...
  • How to set up the Gateway proxy settings
  • How to restart the Gateway Service
  • How to replace the self-signed SSL certificate in ...
  • How to replace a device in EcoStruxure IT Gateway
  • How to disconnect or reconnect a Gateway from EcoS...
  • How to create a device walk file for EcoStruxure I...
  • How to allow a targeted read for Device Support
  • Gathering Gateway logs for troubleshooting
  • Gateway restore fails on some non-English locales
  • Gateway appliance network problems due to bad imag...
  • Gateway Device Communication Alert
  • Galaxy UPS is offline after updating the Gateway
  • Device serial numbers and unique identifiers
  • Device is offline after replacement or RMA
  • Device discover fails - SNMP is disabled by defaul...
  • Cannot discover Redfish devices in Gateway
  • Cannot discover NetBotz devices in Gateway
  • Web server port 443 is being used by another appli...
  • Troubleshooting issues connecting your Gateway to ...
  • Troubleshooting Gateway device discovery failure
  • SNMP walks, Modbus polls, and Redfish discoveries
  • NetBotz devices appear in the list of unknown devi...
  • NetBotz 4.x discovery issue when Gateway proxy set...
  • My device name didn't update in the Gateway after ...
  • My device is not responding - Gateway 1.4.0

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Troubleshooting
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
14756 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Troubleshooting issues connecting your Gateway to EcoStruxure IT

EcoStruxureIT
‎2018-11-13 06:29 AM

Last Updated: JLehr Champion ‎2026-06-12 04:06 AM

 

Common errors with possible causes and recommended actions to help you diagnose and solve issues connecting your Gateway to EcoStruxure IT

 

Connectivity error

 

Unable to resolve host name "{0}". Verify your DNS settings.

Make sure the DNS settings are properly configured in your Gateway server's network preferences.

 

Other well-known sites are reachable. Verify that "{0}" is not blocked by a network filter.

Consult with your IT department to ensure that the us.struxureon.com DNS entry or IP address is added to your firewall rules as they appear to be blocked.

 

Proxy configuration error

 

Proxy server "{0}" cannot be reached or is down.

Double check your proxy configuration settings and contact your IT department to verify the status of the proxy server and its configuration settings.

 

Proxy server name "{0}" cannot be resolved. Check your proxy settings.

Double check your proxy configuration settings and DNS settings and contact your IT department to verify the status of the proxy server and its configuration.

 

Auto-detection is enabled in your proxy settings but no proxies were detected. Try manually setting proxy.

If there is a network proxy between your Gateway server and the outside internet, please configure the proxy settings manually. You'll need the IP address of the proxy server and potentially a username and password if required by your proxy configuration. Your IT department should be able to help you acquire those if they are not directly accessible.

How to set up the EcoStruxure IT Gateway proxy settings

 

Proxy server authentication error

 

Proxy authentication failure. Check your proxy settings.

Confirm that you entered the correct username and password settings for your proxy server.

 

Connection refused

 

Also unable to reach other well-known sites. Check your network connection, or, possible firewall misconfiguration.

Consult with your IT department to ensure that your server is configured correctly to reach the outside internet. A network proxy or firewall could be blocking the connection.

 

Response timeout

Make sure you have a working network connection.

 

Make sure the DNS settings are properly configured in your Gateway server's network preferences.

 

Forbidden

 

Received a forbidden response pointing to a possible proxy misconfiguration.

Double check your proxy configuration settings and contact your IT department to verify the status of the proxy server and its configuration settings.

 

Verify that the time and date values of the operating system of the machine running the EcoStruxure IT Gateway server are properly set. 

 

No route to host

 

Unable to reach configured router at {0}.

Make sure you have a working network connection.

 

No route to host. Check your routing configuration.

Make sure the DNS settings are properly configured in your Gateway server's network preferences.

 

Unknown host

 

Unable to resolve host names for any well-known sites: {0}. Verify your DNS settings.

Make sure the DNS settings are properly configured in your Gateway server's network preferences.

 

Untrusted SSL certificate

 

Certificate is expired or untrusted. Common Name (CN) does not match the URL address.

Check the certificate details to see if it has expired.

 

The certificate might be in the wrong place in the file system.

 

If the certificate was issued by a trusted authority, you may need to install one or more intermediate certificates.

 

With assistance from your IT group, make sure the Certificate Authority used by the proxy is added to the Cloud connectivity > Proxy settings option in the Gateway user interface, or add us.struxureon.com to the exemption list so its traffic is not intercepted.

How to solve the Gateway untrusted certificate chain error

 

Invalid SSL certificate

 

The Gateway appears to be configured to use a proxy that is using SSL interception, and the Gateway does not trust the certificate the Proxy is replacing.

With assistance from your IT group, make sure the Certificate Authority used by the proxy is added to the Cloud connectivity > Proxy settings option in the Gateway user interface, or add us.struxureon.com to the exemption list so its traffic is not intercepted.

 

Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

Comments
iti
iti
Explorer
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2024-10-08 11:02 AM

i ll install ecodial on my pc but not work with microsoft edge123.jpeg

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore