Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Cannot discover NetBotz devices in Gateway

Troubleshooting

How to troubleshoot and solve issues configuring the EcoStruxure IT Gateway

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Gateway
  • Troubleshooting
  • Cannot discover NetBotz devices in Gateway
Options
  • Subscribe to RSS Feed
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Troubleshooting
Options
  • Subscribe to RSS Feed
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1891 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cannot discover NetBotz devices in Gateway

Picard EcoStruxureIT
‎2021-07-15 03:38 AM

Support for unsafe ciphers was removed as part of a security update in EcoStruxure IT Gateway version 1.8.0. NetBotz 4.x devices must now support 2048 bit certificates. 

Symptom

Devices that do not meet this requirement do not discover in Gateway 1.8.0 and newer. There is no indication of a certificate error when you run a new discovery.

When you update your Gateway from a previous version, NetBotz devices are listed as offline.

Resolution

Install a new 2048 bit certificate on the NetBotz device. Self-signed automatically generated SSL certificates use 2048-bit encryption as of NetBotz version 4.5.4.

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of