Cannot discover NetBotz devices in Gateway
Troubleshooting
How to troubleshoot and solve issues configuring the EcoStruxure IT Gateway
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Support for unsafe ciphers was removed as part of a security update in EcoStruxure IT Gateway version 1.8.0. NetBotz 4.x devices must now support 2048 bit certificates.
Symptom
Devices that do not meet this requirement do not discover in Gateway 1.8.0 and newer. There is no indication of a certificate error when you run a new discovery.
When you update your Gateway from a previous version, NetBotz devices are listed as offline.
Resolution
Install a new 2048 bit certificate on the NetBotz device. Self-signed automatically generated SSL certificates use 2048-bit encryption as of NetBotz version 4.5.4.