Weather station programming

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Weather station programming
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
FZetina
Commander FZetina Commander
29
View All
Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
mostafa_ramadan
Ensign mostafa_ramadan
Ensign

Posted: ‎2024-06-13 02:58 AM . Last Modified: ‎2024-07-14 11:38 PM

0 Likes
11
2162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-13 02:58 AM

Weather station programming

Hello,

We need to control facade lighting (Dali Value) with weather station MTN682991 and brightness sensor MTN663593.

I select brightness sensor as sensor type (as attached pic.1)

now how to program Dali value object to this sensor input.

 

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Attachments
Labels
  • Labels:
  • SpaceLYnk
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-06-25 07:54 AM

1 Like
0
2022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-25 07:54 AM

Hello Mostafa_ramadan,


if you are familiar with scripts ... you can try the following one.
It reacts simply on the normal Lux output (shown in your picture under the section "General").
In case the brightness is under a certain level (in my example 100 Lux), then the DALI-Brightness will be slowly increased. When it is completely dark then the brightness goes to 100%. See attached video.
This works the other way arround also.
With the given requirements ... this would be my first approach. What do you think about it? 

Here the script which reacts on each Lux-Level-Update.

-- Get actual Lux-Value
Lux_Value = event.getvalue()
-- Definition of DALI-Brightness-Value Group-Address
DALI_GA = '35/1/2'
 
-- If Lux-Value
if Lux_Value > 100 then
-- Greater then 100 then switch off (0%), if not already done
grp.checkwrite(DALI_GA, 0)
else
  -- Lower then 100 Lux
  DALI_Value = 100 - Lux_Value
grp.checkwrite(DALI_GA, DALI_Value)
end

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Attachments
Reply
Replies 11
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2024-06-13 09:01 AM . Last Modified: ‎2024-06-13 09:02 AM

0 Likes
0
2138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-13 09:01 AM

Hello

 

With the settings sccording your screenshot you will get 3 communicaiton objects: measured lux value, and two 1-bit objects for threshold 1 and threshold 2. The thresholds objects you can use to switch on and off the light.

 

Not sure if I have understood correctly what you want to achieve. If my answer doesn't help you please give some further details what exactly and how you want to control the DALI light.

Reply
mostafa_ramadan
Ensign mostafa_ramadan
Ensign

Posted: ‎2024-06-22 11:57 PM

0 Likes
0
2101
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-22 11:57 PM

Hello,

I need to control lighting Intensity depend on measured lux value from sensors.

 

Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-06-23 11:17 PM . Last Modified: ‎2024-06-23 11:26 PM

1 Like
0
2088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-23 11:17 PM

@mostafa_ramadan 

 

Normally lighting control is calculated in a sensor like a MTN630919 that is holding an calculation function for this, the sensor you have now doesn’t have that function, you can only use the brightness as a threshold and switch something within the set limits.

 

 

But i don’t recommend to use a weather station anyway as normally with constant light control you measure the conditions in the room including reflection and not an outside measurement that is not representing the desired 500 lux in a room itself. 

Just my 50ct..

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-06-24 12:03 AM

0 Likes
1
2081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-24 12:03 AM

Hello Mostafa_ramadan,

quick question ...
Do you have a Wiser for KNX (LSS100100) or a spaceLYnk within your installation?

 

Kind regards
Thomas

Application Design Engineer
Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-06-24 12:24 AM

0 Likes
0
2078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-24 12:24 AM

Hi Thomas, i thought about this option and yes you can make script with certain thresholds to make a mapping with outside measurement 30.000 -> 50% output to DALI or whatever but i don’t think this will ever function properly as you don’t know the room conditions..

 

However this could be a “quick and dirty” implementation i would not recommend to go that way….

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-06-24 11:20 PM

0 Likes
2
2047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-24 11:20 PM

Hi Erwin,

maybe I missunderstood something but I do not understand "room conditions"?
The question is "We need to control facade lighting (Dali Value) with weather station MTN682991 and brightness sensor MTN663593." ... or?
In my understanding he needs to iluminate the facade (outside) of a certain building. 
But maybe I am wrong with it. @mostafa_ramadan , please correct me if I am wrong.

 

Kind regards
Thomas

Application Design Engineer
Reply
mostafa_ramadan
Ensign mostafa_ramadan
Ensign

Posted: ‎2024-06-25 02:36 AM

0 Likes
1
2038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-25 02:36 AM

Hi @Thomas_Rohde,

You are right I need to control outside facade dali fixtures and yes we have spacelynk and AS-P in project.

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-06-25 07:54 AM

1 Like
0
2023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-25 07:54 AM

Hello Mostafa_ramadan,


if you are familiar with scripts ... you can try the following one.
It reacts simply on the normal Lux output (shown in your picture under the section "General").
In case the brightness is under a certain level (in my example 100 Lux), then the DALI-Brightness will be slowly increased. When it is completely dark then the brightness goes to 100%. See attached video.
This works the other way arround also.
With the given requirements ... this would be my first approach. What do you think about it? 

Here the script which reacts on each Lux-Level-Update.

-- Get actual Lux-Value
Lux_Value = event.getvalue()
-- Definition of DALI-Brightness-Value Group-Address
DALI_GA = '35/1/2'
 
-- If Lux-Value
if Lux_Value > 100 then
-- Greater then 100 then switch off (0%), if not already done
grp.checkwrite(DALI_GA, 0)
else
  -- Lower then 100 Lux
  DALI_Value = 100 - Lux_Value
grp.checkwrite(DALI_GA, DALI_Value)
end

Kind regards
Thomas

Application Design Engineer
Attachments
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-07-08 06:40 AM

0 Likes
0
1920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-08 06:40 AM

Hello Mostafa_ramadan,

does it work, or did you found another solution?

 

Kind regards
Thomas

Application Design Engineer
Reply
DkShree
Crewman DkShree
Crewman

Posted: ‎2025-07-25 08:28 AM

0 Likes
1
868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-25 08:28 AM

hello

@Thomas_Rohde sir

 

thanks for your script for lux to Dali lights group. you script I have added in our controller (lss100100) working fine and this script inversely proportional to Light Brightness.

 

here sir I want to add some our requirements for our experience center .

1. if lights lux value between 4000 to 5000 then this scene will trigger or for evening if lux value 500 to 400 then this scene will trigger. i have make number of scenes all scenes working with time like 5 pm 6am and lunch 2 pm. but I want to control from lux value for lux I have installed weather station.

2. if outer temperature or between 27'c to 25'c then following ac will ON and set temperature to 24'c

 

sir can you please share some script for above requirements this will be very helpful for our experience center

 

 

thanks 

Dinesh Kumar Sain

  

 

 

 

 

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2025-07-29 12:48 AM

0 Likes
0
845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-29 12:48 AM

Hello Dinesh!
Can you please be more specific with your request number one?
Sorry, but I do not understand it clearly. Perfect would be a diagram or a table to identify clearly what should happen and when.

Related to point 2
Here the script:

--------------------------------------------------------------------------------------------------
--------------------------------------------------------------------------------------------------
-- Description: Analyses a temperature and depending on a certain temperature range a defined 
-- Setpoint Temperature needs to be send out
--------------------------------------------------------------------------------------------------
-- Skript needs to be placed within \Scripting\Event-based. 
-- The skript needs to be linked with the GA of the dedicated measured temperature.
-- The script will check the measured temperature and within a certain temperature range a 
-- defined setpoint temperature will be sent out.
--------------------------------------------------------------------------------------------------
--------------------------------------------------------------------------------------------------
 
--------------------------------------------------------------------------------------------------
-- NEEDS TO BE ADAPTED! --------------------------------------------------------------------------
-------------------------------------------------------------------------------------------------- 
 
GA_SetPointTemperature = '43/1/2' -- GA needs to be adapted
SetPointTemperature = 24
TemperatureRangeHigh = 27
TemperatureRangeLow = 25
 
--------------------------------------------------------------------------------------------------
-- DONT CHANGE CODE BELOW ------------------------------------------------------------------------
--------------------------------------------------------------------------------------------------
CurrentTemperature = event.getvalue() -- Get actual temperature
 
if (CurrentTemperature > TemperatureRangeLow and CurrentTemperature < TemperatureRangeHigh) then
grp.checkwrite(GA_SetPointTemperature, SetPointTemperature)
end
Kind regards
Thomas

Application Design Engineer
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore