Hello everybody,
I'd need to RESET COUNTERS in Schneider electricity meter iEM3155 via ModBus in W4K.
In W4K in pre-installed MB profile related to iEM3155 is only possibility to read values. Reset should be done by ModBus 16 write function.
I know I can download prepared .json profile and customize it... problem is I'm not able to add there a MB16 write function and make it works. To be concrete:
ModBus 16 function - multiple write:
reg. 5250 (uint16) - write value 2023
reg. 5251 (uint16) - write value 0
Have you ever faced the same issue? If you have an example (.json profile) - would be appreciated! 🙂
Thank you and have a nice day,
Jan
Link copied. Please paste this link to share this article on your social media post.
require('luamodbus')
mb = luamodbus.tcp()
mb:open('192.168.1.2', 502)
mb:connect()
mb:setslave(1) -- Enter the correct Modbus slave address of the kWh meter
--see iEM 3255 user manual from page 62 for possible parameters
-- Reset partial energy counters
datanumber = 2020
reservedalways = ''
mb:writeregisters(5249, datanumber, reservedalways) --max 123 parameters entered by , , , ,
--Register 5250 = Requested command, 5251 = Not used, 5252 = parameter 1
-- Results of Reset partial energy counters
r1, r2 = mb:readregisters(5374, 2)
log ("Result Command: " .. r1)
log ("Result Code: " .. r2) -- 0 = valid operation, 3000 = invalid Operation, 3001 = Invalid Parameter, 3002 = Invalid number of parameters, 3007 = Operation not perfomed
-- ********************************************************
mb:close()
Link copied. Please paste this link to share this article on your social media post.
require('luamodbus')
mb = luamodbus.tcp()
mb:open('192.168.1.2', 502)
mb:connect()
mb:setslave(1) -- Enter the correct Modbus slave address of the kWh meter
--see iEM 3255 user manual from page 62 for possible parameters
-- Reset partial energy counters
datanumber = 2020
reservedalways = ''
mb:writeregisters(5249, datanumber, reservedalways) --max 123 parameters entered by , , , ,
--Register 5250 = Requested command, 5251 = Not used, 5252 = parameter 1
-- Results of Reset partial energy counters
r1, r2 = mb:readregisters(5374, 2)
log ("Result Command: " .. r1)
log ("Result Code: " .. r2) -- 0 = valid operation, 3000 = invalid Operation, 3001 = Invalid Parameter, 3002 = Invalid number of parameters, 3007 = Operation not perfomed
-- ********************************************************
mb:close()