Spacelynk Firmware 2.5.0 issue

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Spacelynk Firmware 2.5.0 issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All
Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic KNX Forum
Start a Topic
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2020-07-09 04:32 AM . Last Modified: ‎2024-07-14 11:48 PM

0 Likes
16
1976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 04:32 AM

Spacelynk Firmware 2.5.0 issue

Hello everyone

 

when I upgrade spacelynk firmware from version 2.4.0 to 2.5.0 its CPU/IO value increases even though I am not using it. 

also, I didn't add any script so its not a script issue. 

I notice this rise when I use the new Touch 3, but even when I remove it the issue still exist  

 

did anyone use the new firmware and face this problem?

 

 

Best Regards,
  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • SpaceLYnk
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 16
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2020-07-09 04:35 AM

0 Likes
3
1974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 04:35 AM

Hi,

 

Have you used a beta version of 2.5.0?

 

I'ts a know issue when you have tested the beta as it had a bug in the Touch 3 daemon and it should not rise when you never have runned the beta, there is a solution but need more info..

 

BR,

 

Erwin

Tags (1)
  • Tags:
  • english
Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2020-07-09 04:42 AM

0 Likes
2
1970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 04:42 AM

thanks, @Erwin-vd-Zwart  for the fast response.

 

I downloaded  the 2.5.0 firmware from here https://www.se.com/ww/en/product/LSS100200/spacelynk-logic-controller/

 

But it not mentioned that this is a beta version 

Best Regards,
Tags (1)
  • Tags:
  • english
Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2020-07-09 04:44 AM

0 Likes
1
1966
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 04:44 AM

No, this is the official, we did some limited BETA testing and that was not distributed by the website..

 

Do you know how to open the Apps FTP folder?

Tags (1)
  • Tags:
  • english
Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2020-07-09 04:49 AM . Last Modified: ‎2020-07-09 04:50 AM

0 Likes
0
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 04:49 AM

No, I don't

Best Regards,
Tags (1)
  • Tags:
  • english
Reply
David_Navratil
Lt. Commander David_Navratil Lt. Commander
Lt. Commander

Posted: ‎2020-07-09 04:51 AM

0 Likes
11
1955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 04:51 AM

Hello,

 

We have upgraded several controllers to the 2.5.0 and we do not see any issues similar to what you are describing.

 

Anyway, we have one small bug in the release 2.5.0 (not really connected to the issue you experiencing) and we release fix version 2.5.1. It is available on the Yammer group or Schneider official web site. Please upgrade FW to the latest one and check if there is any change in CPU load or not.

 

Please send us a project back-up if possible to check if there is any scripting that causing these issues after the upgrade.

 

Thank you

David

Tags (1)
  • Tags:
  • english
Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2020-07-09 04:58 AM . Last Modified: ‎2020-07-09 05:41 AM

0 Likes
10
1948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 04:58 AM

Hi David,

 

I had the same, removing Touch is the solution, but i runned the beta so that makes sense...

 

BR,

 

Erwin

Tags (1)
  • Tags:
  • english
Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2020-07-09 05:07 AM

0 Likes
9
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 05:07 AM

I remove the touch app and stop all scripts 

I will monitor the CPU for a while and check if the problem solved 

 

thanks, @Erwin-vd-Zwart, @David_Navratil 

Best Regards,
Tags (1)
  • Tags:
  • english
Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2020-07-09 05:24 AM . Last Modified: ‎2020-07-09 07:27 AM

0 Likes
8
1936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 05:24 AM

the CPU still loaded it reaches more than 0.7 with no use

 

the only thing changed after upgrade to V2.5.0 was adding new scenes with virtual trigger object, I don't know if this has any effects Capture.JPG

Best Regards,
Tags (1)
  • Tags:
  • english
Reply
Horacio1
Lieutenant JG Horacio1 Lieutenant JG
Lieutenant JG

Posted: ‎2022-02-09 04:33 PM

0 Likes
7
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-09 04:33 PM

I just had an issue with the 2.5.1 firmware upgrade for spacelynk. I previously had the 2.4 firmware in a 3.1 spacelynk HW, I did the upgrade to 2.5.1 and the spacelynk got, sort of stuck, with its top green led blinking at a one each like two senconds rate, but the bottom led doesnt even blink, I already tried a factory reset and a powercycle but the device has the same led blinking pattern.

 

any of you have had any similar experience, if so, how did you solve the problem??

 

Right now I have a client waiting for its system.

 

I hope you can give an idea on how to fix this problem.

 

Regards,

 

 

Tags (1)
  • Tags:
  • english
Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2022-02-09 11:36 PM . Last Modified: ‎2022-02-09 11:42 PM

0 Likes
6
1883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-09 11:36 PM

Looks like there went something wrong during the upgrade, i have done a lot (uncountable) upgrades and that never went wrong, did you interrupt the power somehow?

 

There was a version a FW version that took quite a while before it became accessible due to trend recalculation to a new format, but this is only when having a lot of trends and i think it was older FW then 2.4 to 2.5..not sure so need to look that up,  if you have a lot of trends then please give it time (can be more then a hour) to recalculate them.

 

If you don’t have trends and keep stuck then you might need to reflash the SD card. All data is lost when doing that so you need to have a recent backup.

 

See this document: https://download.schneider-electric.com/files?p_enDocType=Application+solutions&p_File_Name=AN2_001_...

Tags (1)
  • Tags:
  • english
Reply
domotiqa
Lt. Commander domotiqa
Lt. Commander

Posted: ‎2022-02-09 11:50 PM

0 Likes
0
1878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-09 11:50 PM

I had several issue in the past on some Spacelynk/homelynk. If trying to jump from older FW to newest and have bug after upgrading. The solution was to inject update step by step. For example: 2.5.0 then 2.5.1 then 2.5.2

Smarthome & Smartbuilding Expert
Tags (1)
  • Tags:
  • english
Reply
Horacio1
Lieutenant JG Horacio1 Lieutenant JG
Lieutenant JG

Posted: ‎2022-02-10 03:50 AM

0 Likes
0
1874
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-10 03:50 AM

Thanks for your prompt answer!!!

 

I didnt interrupt the process but after more than an hour the device it is still stuck, today I will go to the jobsite again, if it is still stuck I will apply the procedure that share with me.

 

 

Regards,

Tags (1)
  • Tags:
  • english
Reply
Horacio1
Lieutenant JG Horacio1 Lieutenant JG
Lieutenant JG

Posted: ‎2022-02-11 09:39 AM

0 Likes
3
1870
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-11 09:39 AM

Thanks for the help!!!

 

I did the procedure mentioned, but right now the spacelynk doesn't even have a bliking LED.

 

(i have attached a video of the LED status after the upgrade)

 

Any suggestions? besides applying the guaranty,

 

Regards,

HSU

Attachments
Tags (1)
  • Tags:
  • english
Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2022-02-11 10:27 AM

0 Likes
2
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-11 10:27 AM

What did you transfered to the SD card? The sL_HW2_xx_3_xx_recovery.img.gz file?

 

You need to extract rec2.img (947 Mb) from sL_HW2_xx_3_xx_recovery.img.gz (with 7zip or similiar tool) and then use USB Image Tool to restore rec2.img to the SD card, insert the SD card to the controller, boot it up, open the browser to 192.168.0.10 and you should get a popup reqeusting to select the FW you want to load, then select the latest FW spaceLYnk-2.7.0_hw2.xx_hw3.xx.img, reboot again and all should be as new out of the box on 192.168.0.10

Tags (1)
  • Tags:
  • english
Reply
Horacio1
Lieutenant JG Horacio1 Lieutenant JG
Lieutenant JG

Posted: ‎2022-02-11 11:38 AM

0 Likes
1
1865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-11 11:38 AM

Thanks!!!

now it is on, I mean the led n°1 is blinking, at like 1 beat per second, how long should it take to left the spaclynk operative?? so far it has been 20 minutes in this state...

Tags (1)
  • Tags:
  • english
Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2022-02-11 11:54 AM

0 Likes
0
1863
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-11 11:54 AM

Can you try clearing browser cache or incognito? You should get a popup requesting to select your FW

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore