SpaceLynk lost data from trend logs when have the power interrupted

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • SpaceLynk lost data from trend logs when have the power interrupted
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
FZetina
Commander FZetina Commander
29
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
sesa273291
sesa273291 Cadet
Cadet

Posted: ‎2024-08-26 02:10 AM

0 Likes
2
693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-26 02:10 AM

SpaceLynk lost data from trend logs when have the power interrupted

Hi!

 

SpaceLynk


Then, when the power supply to the SpaceLynk module is interrupted, it loses all stored data in trend logs starting at 00:00 of the current day until the voltage is restored.

Question: is the data from 00:00 saved in the operative memory and only after a 24-hour cycle written in the independent memory? What is the reason for data loss?

Labels
  • Labels:
  • SpaceLYnk
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-08-26 09:21 PM . Last Modified: ‎2024-08-26 10:38 PM

0 Likes
1
643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-26 09:21 PM

To protect the SD card from extensive usage (and get corrupted in the end) the controller saves al configuration on a 15 minute interval (i thought 30 minutes but manual states 15), but the trend saving is based on the total trend size, how bigger the total trend size is set how longer the save interval is, so yes what you notice is correct and is functioning as designed.

 

This is from the release notes 2.1.1:

 

Save Interval.jpg

If you want to prevent this from happening than you should use a form of UPS to avoid you controller to restart by power failure, a manual restart from the OS will save everything first.

See Answer In Context

Reply
Replies 2
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-08-26 09:21 PM . Last Modified: ‎2024-08-26 10:38 PM

0 Likes
1
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-26 09:21 PM

To protect the SD card from extensive usage (and get corrupted in the end) the controller saves al configuration on a 15 minute interval (i thought 30 minutes but manual states 15), but the trend saving is based on the total trend size, how bigger the total trend size is set how longer the save interval is, so yes what you notice is correct and is functioning as designed.

 

This is from the release notes 2.1.1:

 

Save Interval.jpg

If you want to prevent this from happening than you should use a form of UPS to avoid you controller to restart by power failure, a manual restart from the OS will save everything first.

Reply
sesa273291
sesa273291 Cadet
Cadet

Posted: ‎2024-08-26 11:25 PM

0 Likes
0
620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-26 11:25 PM

Thank you!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore