Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

SpaceLynk LSS100200 modbus visualization

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • SpaceLynk LSS100200 modbus visualization
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
Andreabolis98
Andreabolis98
Cadet

Posted: ‎2024-08-08 09:20 PM

0 Likes
1
913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-08 09:20 PM

SpaceLynk LSS100200 modbus visualization

 

Hi everyone,
I am new on Spacelynk platform, for a new application with SpacLynk LSS 100200 i need to:
- read and write a list of holding register from 4 modbus server device (with different id);
- i dont have a KNX network connected to the SpaceLynk.
- visualization via webserver the data come from Modbus

- create scenario and scheduler.

My questions are:
- can i comunicate with 4 modbus server devices simultaneously?
- in webserver Widgets, can i read and write directly the modbus variables or i have to convert before in knx group?
- for schedule, scenario and visualization, is it a problem if i dont have a real knx network connected to the spaceLink? or its enough to create a vistual object on knx ?
- is there an offline configurator? At the moment i dont have spaceLynk phisically.

Thanks.

Best regards

Labels
  • Labels:
  • SpaceLogic devices
  • SpaceLYnk
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
alexcarey
Crewman alexcarey
Crewman

Posted: ‎2024-08-09 03:26 AM . Last Modified: ‎2024-10-02 10:24 PM

0 Likes
0
902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-09 03:26 AM


@Andreabolis98 wrote:

 

Hi everyone,
I am new on Spacelynk platform, for a new application with SpacLynk LSS 100200 i need to:
- read and write a list of holding register from 4 modbus server device (with different id);
- i dont have a KNX network connected to the SpaceLynk.
- visualization via webserver the data come from Modbus

- create scenario and scheduler.

My questions are:
- can i comunicate with 4 modbus server devices simultaneously?
- in webserver Widgets, can i read and write directly the modbus variables or i have to convert before in knx group?
- for schedule, scenario and visualization, is it a problem if i dont have a real knx network connected to the spaceLink? or its enough to create a vistual object on knx ?
- is there an offline configurator? At the moment i dont have spaceLynk phisically.

Thanks.

Best regards


Hi,

  1. Modbus Communication: Yes, you can communicate with multiple Modbus server devices simultaneously with SpacLynk LSS 100200.

  2. Webserver Widgets: Widgets on the webserver can read and write Modbus variables directly without needing to convert them to KNX groups.

  3. KNX Network: You can still create schedules, scenarios, and visualizations without a physical KNX network. Virtual KNX objects should be sufficient.

  4. Offline Configurator: SpacLynk typically does not offer an offline configurator. You might need to wait until you have physical access to the SpacLynk device for full configuration.

fire kirin
nulls brawl download apk

See Answer In Context

Reply
Reply 1
alexcarey
Crewman alexcarey
Crewman

Posted: ‎2024-08-09 03:26 AM . Last Modified: ‎2024-10-02 10:24 PM

0 Likes
0
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-09 03:26 AM


@Andreabolis98 wrote:

 

Hi everyone,
I am new on Spacelynk platform, for a new application with SpacLynk LSS 100200 i need to:
- read and write a list of holding register from 4 modbus server device (with different id);
- i dont have a KNX network connected to the SpaceLynk.
- visualization via webserver the data come from Modbus

- create scenario and scheduler.

My questions are:
- can i comunicate with 4 modbus server devices simultaneously?
- in webserver Widgets, can i read and write directly the modbus variables or i have to convert before in knx group?
- for schedule, scenario and visualization, is it a problem if i dont have a real knx network connected to the spaceLink? or its enough to create a vistual object on knx ?
- is there an offline configurator? At the moment i dont have spaceLynk phisically.

Thanks.

Best regards


Hi,

  1. Modbus Communication: Yes, you can communicate with multiple Modbus server devices simultaneously with SpacLynk LSS 100200.

  2. Webserver Widgets: Widgets on the webserver can read and write Modbus variables directly without needing to convert them to KNX groups.

  3. KNX Network: You can still create schedules, scenarios, and visualizations without a physical KNX network. Virtual KNX objects should be sufficient.

  4. Offline Configurator: SpacLynk typically does not offer an offline configurator. You might need to wait until you have physical access to the SpacLynk device for full configuration.

fire kirin
nulls brawl download apk
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore