SpaceLogic LSS100300 gateway

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • SpaceLogic LSS100300 gateway
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic KNX Forum
Start a Topic
ElvisOla
Crewman ElvisOla
Crewman

Posted: ‎2025-10-10 03:18 AM

1 Like
9
700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-10 03:18 AM

SpaceLogic LSS100300 gateway

Hello team.

I added the KNX spacelogic BMS IP Gateway module (LSS100300) to the Bacnet interface in the EBO 2024 software version 6.0.3.112 under the AS-B-24-P control unit. How can I display the CIAT air conditioners that are connected in KNX serial mode on the LSS100300? I cannot find the KNX section in the EBO software settings or in the LSS100300 properties. Do I need to load a KNX driver to detect or manually add the air conditioners? If so, please guide me on how to do this.

Translated with DeepL.com (free version)

Labels
  • Labels:
  • Other
  • SpaceLogic devices
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2025-10-28 06:23 AM

0 Likes
8
608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-28 06:23 AM

Hello ElvisOla!

To "How can I display the CIAT air conditioners that are connected in KNX serial mode on the LSS100300?"
You need to import into the LSS100300 either the dedicated ETS-Project or only the Group-Address-Export.
With both ways you implement simply the dedicated GA and you can decide which GA's you really need for the exchange between KNX+BACnet.
Of course you need to adapt within LSS100300 the dedicated BACnet-Server details.

Sounds like a plan?!

Kind regards
Thomas

Application Design Engineer
Reply
Cristiano_Carli_Ballola
Lt. Commander Cristiano_Carli_Ballola Lt. Commander
Lt. Commander

Posted: ‎2025-10-28 11:26 PM

2 Likes
7
598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-28 11:26 PM

Hallo@ElvisOla

 

here are some steps you have to follow 

1- import your ETS project into the BMS IP GATEWAY. Now you should see all the planned group addresses within the KNX object section 

2- select which of those KNX objects should be exported to the BACNet interface. Simply click on the dedicated “export” checkbox.

3- Navigate into the System/Interface/BACnet menu and set all the necessary fields like BACnet ID, BACnet Name etc.

4- Open your Building Operation workstation, select you AS and use the Device Discovery function to detect your BMS GATEWAY. 

5- Drag the BMS GATEWAY within your AS BACnet IP network. 
6- right click on the BMS GATEWAY within the BACnet interface, then select the device/upload all objects menu. All the selected KNX objects should be now listed as BACnet objects 

 

 

Reply
ElvisOla
Crewman ElvisOla
Crewman

Posted: ‎2025-11-05 02:25 AM

0 Likes
6
529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-05 02:25 AM

Hello Cristiano
I am attaching a video and a screenshot of what happens when I try to import the knxpro file sent to me by the manufacturer of CIAT air conditioners.
The import was done from the gateway's web interface and it is not working.

I have already added the LSS100300 under AS in EBOW.
Thank you for your help.
Please help.

Attachments
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2025-11-06 12:20 AM

0 Likes
5
521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-06 12:20 AM

Hello ElvisOla!

Is the ETS-Project protected with a password?
Would you mind to share the ETS-Project?

 

Kind regards
Thomas

Application Design Engineer
Reply
ElvisOla
Crewman ElvisOla
Crewman

Posted: ‎2025-11-10 12:34 AM

0 Likes
4
464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-10 12:34 AM

Hello Thomas Rhode

No, the knxpro files do not have a password and were sent to me by the manufacturer of CIAT air conditioners. Attached is the compressed file sent by the manufacturer, which I have unzipped. I tried several, but none of them worked. Or is the ETS file you are referring to different from the KNXPRO file?

Attachments
Fiches param knxproj.zip
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2025-11-10 07:49 AM

1 Like
3
449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-10 07:49 AM

Hello ElvisOla!

 

I have checked the first project out of the many ones you sent.
By doing so, I saw that this ETS-Project consists only out of one device.
And I guess the parameter settings are still unchanged (Default).


However … the blocking point here is, that there is no group-address linked to any of the objects.
There is not even created a single KNX Group Address.
The KNX-Group-Addresses are the essential details which the KNX BMS IP Gateway takes out of the ETS-Project!
If no Group-Address is part of your project, it does not make sense to import, it which leads to the error message.


I guess the best way of support would be to go in local contact with a SE KNX Specialist.
In which country are you located?

Kind regards
Thomas

Application Design Engineer
Reply
ElvisOla
Crewman ElvisOla
Crewman

Posted: ‎2025-11-11 06:11 AM

0 Likes
1
408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-11 06:11 AM

Hello Thomas Rohde,

Thank you for your reply.
I would like you to help me get in touch with a KNX SE specialist who can help me finalize the KNXPRO file. I am in Benin (West Africa).
If possible, I would appreciate your help or guidance on how to create the KNX GROUP ADDRESS to import the file and resolve the issue.
All air conditioners are CIAT brand and have a KNX port connected in bus mode to the LSS100300 control unit.

Thank you very much for your response.

 

Reply
Quintus23
Quintus23
Cadet

Posted: ‎2025-11-18 12:38 AM

0 Likes
0
327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-18 12:38 AM

Hey,

Are your CIAT controllers V3000 models? If so, not all KNX variables can be converted to BACNET, for example the 3 x 2 bytes.

Good luck !

Reply
ElvisOla
Crewman ElvisOla
Crewman

Posted: ‎2025-11-18 01:24 AM

0 Likes
0
320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-18 01:24 AM

Hello Thomas Rohde,

I replied to you last Monday, but I don't know if you saw my message.I would like you to help me get in touch with a KNX SE specialist who can help me finalize the KNXPRO file. I am in Benin (West Africa).
If possible, I would appreciate your help or guidance on how to create the KNX GROUP ADDRESS to import the file and resolve the issue.
All air conditioners are CIAT brand and have a KNX port connected in bus mode to the LSS100300 control unit.

Thank you very much for your response.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore