Some Group objects disappeared from DALI GW

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Some Group objects disappeared from DALI GW
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2022-07-24 03:24 AM . Last Modified: ‎2024-07-14 11:44 PM

0 Likes
6
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-24 03:24 AM

Some Group objects disappeared from DALI GW

Hello 

I Have DALI GW MTN6725-0101

I Link GA to Group objects, then I notice that some group objects dissipated except failure status!

please see attached image 

DALI GA.JPG

Best Regards,
  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • Documents
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2022-07-27 06:41 AM

0 Likes
2
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-27 06:41 AM

Hello IC-Systems!

I am not sure to get your question in the right way (but here is a question why I couldn't control each ECG in the group?)
There are two ways to control DALI-ECGs in principal.


1. Single ECG Control
As this small words are already explaining, using this method you can control each single ECG seperately and you get the dedicated GA's to do so.

2. Group Control
This method saves time in case you have several lights control in one shot (e.g. general light in a big open office) with many ECGs.
The idea behind is to put them together in one "Group" to make the comissioning and control easy.

If you want to combine both ways you need to select the single ECG Approach and you make the "grouping" by the help of dedicated GA's.


Kind regards
Thomas

Application Design Engineer

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 6
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2022-07-24 11:56 PM

1 Like
1
825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-24 11:56 PM

Hello IC-Systems,

 

can you please explain a bit more in detail the steps you did to better understand your case.
Can you please share the FW-Version of the DALI-GW?
Maybe it would be helpfull to get the ETS-Project also.

 

Kind regards
Thomas

Application Design Engineer
Tags (1)
  • Tags:
  • english
Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2022-07-25 11:20 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-25 11:20 PM

Hello @Thomas_Rohde 

I added the DALI GW from the ETS Library, then I connected the GA's

In the site I used the DCA to deal with the DALI Bus, test the DALI ECG's, and download the configurations.

then when I start to program Keypads, TS I noticed that some Group objects were disappeared.

 

some of these DALI GWs which has this issue was in error but some DALI GW with no error has the same issue.

 

regarding FW I will send it ASA I have it from the site.

 

I will send you the ETS File VIA PM its built in ETS5 

Best Regards,
Tags (1)
  • Tags:
  • english
Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2022-07-26 12:17 AM

0 Likes
3
815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-26 12:17 AM

 

oops its related to grouping.

each ECG Linked to a group its individual group objects will disappeared.

 

but in the MTN6725-0001 GW when you connect ECG to a group a warning pop up tells you that this modification may unlink group addresses!.

 

but in the Spacelogic GW there is no pop up warning

 

but here is a question why I couldn't control each ECG in the group?

Best Regards,
Tags (1)
  • Tags:
  • english
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2022-07-27 06:41 AM

0 Likes
2
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-27 06:41 AM

Hello IC-Systems!

I am not sure to get your question in the right way (but here is a question why I couldn't control each ECG in the group?)
There are two ways to control DALI-ECGs in principal.


1. Single ECG Control
As this small words are already explaining, using this method you can control each single ECG seperately and you get the dedicated GA's to do so.

2. Group Control
This method saves time in case you have several lights control in one shot (e.g. general light in a big open office) with many ECGs.
The idea behind is to put them together in one "Group" to make the comissioning and control easy.

If you want to combine both ways you need to select the single ECG Approach and you make the "grouping" by the help of dedicated GA's.


Kind regards
Thomas

Application Design Engineer
Tags (1)
  • Tags:
  • english
Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2022-07-30 02:12 AM

0 Likes
1
809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-30 02:12 AM

Hello @Thomas_Rohde 

But I think this principle is not related to the DALI Protocol, I mean DALI Protocol allow control individual ECGs in a Group.

but on/off feedback and value feedback issues will rise up here.

 

Am I right? 

 

BR,

Best Regards,
Tags (1)
  • Tags:
  • english
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2022-07-31 11:47 PM

1 Like
0
804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-31 11:47 PM

Hello IC-Systems!

 

To be honest ... I am not deeply familar with the DALI-Protocol.
I can just support you on our approach of our DALI-Gateways.

As I understood that you would like to combine both ways of single and group ECG-Control
I think the best way is to go for the single ECG-Control and realize the Group-Function
with the help of dedicated Group-Addresses on the KNX-Side.

 

Kind regards
Thomas

Application Design Engineer
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore