PowerTag.json
Hello,
I've created and verified Modbus profile for PowerTags. The profile is based on unofficial Modbus profile by Quentin Leddet. Feel free to use the profile.
Modbus addresses for Power Tags (max. 20) are dynamically allocated from 150 to 169. Registers are always the same. There is not implemented Acti9 - Smartlink SI B (A9XMZA08) in Wiser for KNX and spaceLYnk in actual firmware.
Nevertheless you can use the one for A9XMEA08 which is already in Modbus profiles. Please do not modify this profile. Acti 9 Smartlink TCP (A9XMEA08) is "hardcoded" in the firmware.