When it comes to the 0-10V FCU application , The FCU controller is not available in the current KNX product range , but by using the latest TC903 or TC907 the integration is possible with the help of SpaceLYnk/Wiser for KNX through Modbus . Attached is the modbus profile for TC90x .
Additional to that , if the system needs to be controlled from the KNX Multi touch Pro , some small scripting is also required to match the Fan speed , Auto and OFF, Attached is the Project Backup
Link copied. Please paste this link to share this article on your social media post.
Thank you, Hashim for the integration guidance. We are going to add a profile to next firmware release together with other in queue.
Link copied. Please paste this link to share this article on your social media post.
does the system alredy have the AC fan speed interlocked internally?
looking at the json file it has 3 different modbus registers for the ac fan speed status, each with on/off value..
is it possible for them all to be "on" ?? or does the product update the other registers automatically to off ?
"name": "Fan speed Status - High", "bus_datatype": "bool", "type": "coil", "address": 4, "writable": 0 , "value_custom": {"0": "Off", "1": "On" }},
{ "name": "Fan speed Status - Medium", "bus_datatype": "bool", "type": "coil", "address": 5, "writable": 0, "value_custom": {"0": "Off", "1": "On" } },
{ "name": "Fan speed Status - Low", "bus_datatype": "bool", "type": "coil", "address": 6, "writable": 0, "value_custom": {"0": "Off", "1": "On" } }
asking for my own info when I need to create jsons for other products..
also noted you typo, I think this should read as 'units'........ not "uints" throughout the json
"uints": "°C" },
some newer people might get confused seeing it as unsigned integer instead of a spelling error.
Link copied. Please paste this link to share this article on your social media post.
Hi @Coppo
The lines you mentioned are the one which are reading coils , this is like a status feedback object in KNX . The register which is used to change the fan speed are as follows . There is an interlock between the 3 output in TC907
{ "name": "Fan Mode", "bus_datatype": "uint16", "type": "register", "address": 5, "writable": true, "value_custom": {"0": "High", "1": "Medium", "2": "Low", "3": "Auto" } },
Thank you for pointing out the typo in the file ,updated above is the new .json. The typo "uints": "°C" as well as "uints": "V" are updated . There were no error in the test and works well with the same but, the correct one is as you have mentioned .
Link copied. Please paste this link to share this article on your social media post.
Hi Hashin,
thnak you for confirming my question that the TC907 has intenral interlocking on those registers, much thanks.
just thought it looked odd as i would normally expect to see it exactly like you posted
{"0": "High", "1": "Medium", "2": "Low", "3": "Auto" } },
all good. much thanks. I will add it to my json library.
we re-use these modules in AU for the Clipsal 5500NAC / SE LSS5500NAC automation controller gateways.