MTN646991 Control unit 0-10 V REG-K/3-gang can not control the 0-10V signal properly

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • MTN646991 Control unit 0-10 V REG-K/3-gang can not control the 0-10V signal properly
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
121
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
54
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
30
FZetina
Lt. Commander FZetina Lt. Commander
27
View All
Related Products
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic KNX Forum
Theodoros
Lieutenant JG Theodoros
Lieutenant JG

Posted: ‎2025-02-05 10:58 PM

0 Likes
1
178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-05 10:58 PM

MTN646991 Control unit 0-10 V REG-K/3-gang can not control the 0-10V signal properly

hi everyone,

So in the datasheet of MTN646991 its saying this device can giving out 0-10V(dc) but i measure it in reality its analog "output" basically just 100k Ohm Potentionmeter, the 10V(dc) is from Load(driver) and the MTN646991 just adjust the voltage of the 0-10V interface.

MTN646991.jpg

 

The problem I encountered was that the device's Potentiometer behaved very strangely. I tested it with 3 different drivers with same lamp (all 4 items are Constant Voltage type) :

1. MEANWELL ELG-240-24B : can not be dimmed

Interface = Signal voltage

- 100%    = 10.04 Vdc

-   50%    = 5.01 Vdc (same brightness as 100%)

-     0%    = 0.08 Vdc (flashing before turn off)

 

2. EUCHIPS EUP12A-1HMC-1 : can be dimmed

Interface = Signal voltage

- 100%    = 9.15 Vdc

-   50%    = 4.77 Vdc (dimmed)

-   15%    = 3.45 Vdc (dimmed)

-     5%    = 0.80 Vdc (dimmed)

-     0%    = 0.00 Vdc (off)

 

3. AIDimming PE-TL150TV24 : can not be dimmed

Interface = Signal voltage

- 100%    = 10.10 Vdc

-   50%    = 5.10 Vdc (same brightness as 100%)

-   10%    = 1.06 Vdc (same brightness as 100%)

-     0%    = 0.06 Vdc (off)

 

I used a Potentiometer to manually control the 0-10V(dc) interface then all 3 drivers all can dim the lamp normally.

 

Theodoros_2-1738824071644.jpeg

 

So the problem is at the MTN646991 analog output...........

 

I tried downloading ETS Application for all 3 types of Dimming Curve but the result is still the same. Does anyone know what the problem is and how to fix it?

Theodoros_0-1738823201302.png

 

  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (1)
Labels
  • Labels:
  • Documents
  • Feedback
  • Protocols
  • SpaceLogic devices
  • SpaceLYnk
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2025-02-06 04:19 AM

1 Like
0
153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-06 04:19 AM

Hello Theodoros!

 

Many THANKS for your feedback first of all.

To "So in the datasheet of MTN646991 its saying this device can giving out 0-10V(dc) but i measure it in reality its analog "output" basically just 100k Ohm Potentionmeter, the 10V(dc) is from Load(driver) and the MTN646991 just adjust the voltage of the 0-10V interface."
Yes, you are correct. We need to adapt this entry as the product does NOT provide a certain voltage by itself.

To "So the problem is at the MTN646991 analog output....."
Actually it looks a bit strange to me. According to the values you measured the device gives good values out.
There is, at least for me in a first glance, only one value beside what I would expect.
And this one is by the one which seems to work correctly (-   15%    = 3.45 Vdc (dimmed)).
I calculated the values how they should be and it gives the following picture.

Thomas_Rohde_0-1738844014795.png

So it seems to me that the resistance value is mostly exactly how it should be.
The question for me in this case is ... Why the two different drivers didnt work?

Please contact our local technical support for further support.
Maybe you could be so kind and borrow the technical support team your drivers for test?
So that they can analyse the problem more in detail.

Please come back here to share the outcome.

 

Kind regards
Thomas

Application Design Engineer
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of