MTN6309xx ARGUS and MTN6276xx Pushbutton ETS Parameter Settings

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • MTN6309xx ARGUS and MTN6276xx Pushbutton ETS Parameter Settings
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
121
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
54
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
30
FZetina
Lt. Commander FZetina Lt. Commander
27
View All
Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Solved
ErkinV
Lieutenant | EcoXpert Master ErkinV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-07-09 11:26 PM . Last Modified: ‎2024-07-14 11:38 PM

0 Likes
7
917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-09 11:26 PM

MTN6309xx ARGUS and MTN6276xx Pushbutton ETS Parameter Settings

Hello Everybody,

 

I have an MTN6309xx ARGUS sensor and an MTN6276xx push button. I would like to use them in a specific way, but I need the ARGUS and push button parameters for ETS. Could you please help me with this?

 

The usage is as follows:

 

The fixture in a room will be controlled by a 2-gang push button where the top buttons will dim and the bottom buttons will turn on/off. However, there is an ARGUS sensor in the room. When activated through the button, the ARGUS sensor will be deactivated and the fixture will not turn off. However, when turned off through the button, the ARGUS sensor will be activated and the fixture will turn on when someone enters the room. Unfortunately, I couldn't make these parameter adjustments, and I urgently need a solution. Could you please help me?

 

@Thomas_Rohde 

@Erwin-vd-Zwart 

 

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • Other
  • SpaceLYnk
  • Wiser for KNX
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-07-10 01:50 AM

0 Likes
2
892
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-10 01:50 AM

Hi ErkinV,

 

I do not have the products next to me to test the configuration I have prepared.
But I think it will work like that. 
Within the attached ETS-Backup you will find three products:
1x MTN6309xx
1x MTN6276xx
1x MTN6710-0102
Each with a minimum setup to focus on the solution we are looking for.
Please let me know if it works as requested and of course if not 😉

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Attachments
PB+PIR in a room.zip
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-07-10 05:27 AM . Last Modified: ‎2024-07-10 06:00 AM

0 Likes
0
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-10 05:27 AM

Hi ErkinV,

you just need to adapt the current 4bit Obj against a 1 byte. 
Then you can e.g. use Button 1 with 80%, Button 2 with 60% and Button 3 with 1 bit  = 1 (100%). All three buttons will activate the lock fct. Only Button 4 with 1 bit  = 0 (0%) will turn of manually the light and deactivate the lock fct..
Of course instead of the Dimm Act. you need to address the dedicated DALI ECG.

 

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Reply
Replies 7
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-07-10 01:50 AM

0 Likes
2
893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-10 01:50 AM

Hi ErkinV,

 

I do not have the products next to me to test the configuration I have prepared.
But I think it will work like that. 
Within the attached ETS-Backup you will find three products:
1x MTN6309xx
1x MTN6276xx
1x MTN6710-0102
Each with a minimum setup to focus on the solution we are looking for.
Please let me know if it works as requested and of course if not 😉

Kind regards
Thomas

Application Design Engineer
Attachments
PB+PIR in a room.zip
Reply
ErkinV
Lieutenant | EcoXpert Master ErkinV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-07-10 05:02 AM

0 Likes
1
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-10 05:02 AM

Hi @Thomas_Rohde,

 

First of all, thank you very much for your efforts and help. However, there is a situation: I gave you incorrect information, which led to a different outcome, and we did not achieve the desired result. Our other module besides the button and ARGUS is the DALI Gateway (MTN6725-0101). We will control the luminaire via DALI, and our button will send the output through DALI. It will turn on and off from 0-100% with Push 1 and 2, and it will be ON/OFF with Push 3 and 4. When the button is active, ARGUS will be disabled; when the button is off, it will work from ARGUS.

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-07-10 05:27 AM . Last Modified: ‎2024-07-10 06:00 AM

0 Likes
0
873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-10 05:27 AM

Hi ErkinV,

you just need to adapt the current 4bit Obj against a 1 byte. 
Then you can e.g. use Button 1 with 80%, Button 2 with 60% and Button 3 with 1 bit  = 1 (100%). All three buttons will activate the lock fct. Only Button 4 with 1 bit  = 0 (0%) will turn of manually the light and deactivate the lock fct..
Of course instead of the Dimm Act. you need to address the dedicated DALI ECG.

 

Kind regards
Thomas

Application Design Engineer
Reply
ErkinV
Lieutenant | EcoXpert Master ErkinV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-07-26 02:29 AM . Last Modified: ‎2024-07-26 06:26 AM

0 Likes
1
772
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-26 02:29 AM

Hi @Thomas_Rohde ,

 

In my system, changes have been made, and in my current setup, I have DALI fixtures with a dim value ranging from 0-100% (1 byte) in my rooms, and there are Argus sensors in the rooms as well. I’m not sure if what I want to do is possible, but here’s what I’m aiming for:

 

  • The 1st and 2nd buttons on my 2-gang switches will dim by giving a value between 0-100 (1 byte).
  • The Argus sensors will do the same.

 

When a person in the room activates the fixture via the button, the Argus sensor will not be active in any way. However, when the button is turned off, the Argus will activate if the light level falls below 50 lux. After the Argus has activated, if the dimming is adjusted via the button, the last value set by the button should become active.

Is it possible to create such a scenario? We’ve tried everything within our knowledge but couldn’t make it work. We are looking for your assistance, or if you have a different scenario in mind, could you explain how we can use it?

 

We would be very grateful for your help. 

 

My ETS knxproj backup is attached.

Attachments
TRT SPOR ANKARA_EV.rar
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-07-30 06:04 AM

0 Likes
0
734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-30 06:04 AM

Hello ErkinV,

I checked your project and I was also thinking in your direction when I saw your requirements.
The problem here is that the logic, inbuilt in this sensors, is not sufficient to handle this "more complex" logic.
It is easily done with the help of a script within W4K/sL but I dont know if you have these devices also within your project?

Kind regards
Thomas

Application Design Engineer
Reply
ErkinV
Lieutenant | EcoXpert Master ErkinV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-07-31 04:14 AM

0 Likes
1
717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-31 04:14 AM

Hello Thomas,

 

Honestly, I'm glad that our sensor can't perform this function because we were thinking that 'it could be done through ETS, but we can't seem to do it.' We are going to use a W4K in our project, but we don't know how to do what you mentioned. We would be very happy if we can do it there.

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-08-06 06:49 AM . Last Modified: ‎2024-08-06 07:16 AM

0 Likes
0
685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-06 06:49 AM

Hello ErkinV,

sorry for the late reply!
Your requirements have not been super clear to me so I took some asssumptions.
E.g. how to handle exactly the second light?
I added also a function that a second Block/Channel within the MotionSensor (MS) will deactivate the lights when office user has switched on the lights but never switch off. So please configure the MS in the way you like in terms of times so that this function is not disturbing but still offers the comfort to switch off the light when nobody is detected maybe for 2 hours or similar. It will unlock also the first Block/Channel again so that the lights will go on automatically in case office user will return.
Attached you will find the needed script with a lot of descriptions/comments.

Please let me know if this works for you.

 

Kind regards
Thomas

Application Design Engineer
Attachments
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of