Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

MTN630819 Sensor for Dimming

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • MTN630819 Sensor for Dimming
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Thomas_Rohde Champion
141
Erwin-vd-Zwart
Erwin-vd-Zwart Champion
63
Heribert_Dölger
Heribert_Dölger Leader
36
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
Horacio1
Horacio1 Explorer
Explorer

Posted: ‎2023-12-14 04:46 PM . Last Modified: ‎2024-07-14 11:41 PM

0 Likes
6
2301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-14 04:46 PM

MTN630819 Sensor for Dimming

Hello KNX Community,

 

I've got a question regarding the MTN630819 sensor for a dimming application that uses DALI lights, can I use the MTN630819 for this kind of application where I have to dim the DALI lights base on the brightness and the presence in a room??? or should I use MTN630919 for this application since it has the light control???

 

have you ever had the experience of using this MTN630819? did you use it with Dimeable lights or just on/off lights?

 

Looking forward to your answers,

 

Regards,

HSU

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • SpaceLYnk
Tags (3)
  • Tags:
  • dali
  • english
  • knx
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Thomas_Rohde Champion
Champion

Posted: ‎2023-12-15 07:04 AM

0 Likes
1
2291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-15 07:04 AM

Hi Horacio1,


To "So to keep a certain level of behavior the best choices is the MTN630919. right?"
Yes correct.
To keep a certain light level in the room, in case of motion is detected, you need to use MTN6309xx.

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Reply
Replies 6
Cristiano_Carli_Ballola
Cristiano_Carli_Ballola Mentor
Mentor

Posted: ‎2023-12-14 11:52 PM

1 Like
0
2298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-14 11:52 PM

Hi!

the brightness dependance light control of the MTN630819 offers you the opportunity to set a brightness threshold and, consequently, switch or dimm a light when the brightness is below that defined level.
On the other hand, If your target is to constantly mantein a specif brightness level within a room, you need to use the MTN630919

In both sensors, the brightness control could be in combination with a presence detection 

Reply
Horacio1
Horacio1 Explorer
Explorer

Posted: ‎2023-12-15 03:12 AM

0 Likes
0
2295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-15 03:12 AM

Thanks for your answer SESA123711_brid, I was asking this because somebody told me that we cant dim the DALI lights with the MTN630819.

do you have an example of the MTN630819 ETS5 configuration you can share???

 

Right now I dont have an MTN630819 in my lab.

 

I appreciate the answers,

 

Regards

Reply
Thomas_Rohde
Thomas_Rohde Champion
Champion

Posted: ‎2023-12-15 05:23 AM

0 Likes
1
2293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-15 05:23 AM

Hi Horacio1,

here a dedicated picture of the ETS.

Thomas_Rohde_0-1702646574560.png

 

 

Kind regards
Thomas

Application Design Engineer
Reply
Horacio1
Horacio1 Explorer
Explorer

Posted: ‎2023-12-15 06:29 AM

0 Likes
0
2292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-15 06:29 AM

Hi Thomas,

thanks for your answer.

Can in the value 0-100% (second comment from the top) use presence as well??

 

The way you describe the behavior seem digital, like just on/off to a certain level of brightness, but can´t keep a level of brightness in the room with this sensor, am I right???

 

and on the other hand the MTN630919 seems to have a more analogic behavior.

 

So to keep a certain level of behavior the best choices is the MTN630919. right?

Reply
Thomas_Rohde
Thomas_Rohde Champion
Champion

Posted: ‎2023-12-15 07:04 AM

0 Likes
1
2292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-15 07:04 AM

Hi Horacio1,


To "So to keep a certain level of behavior the best choices is the MTN630919. right?"
Yes correct.
To keep a certain light level in the room, in case of motion is detected, you need to use MTN6309xx.

Kind regards
Thomas

Application Design Engineer
Reply
esteve_budia
esteve_budia Mentor
Mentor

Posted: ‎2023-12-21 11:32 PM

1 Like
0
2283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-21 11:32 PM

MTN630919 Is a really amazing detector able to do this constant regulation and more, more, more... It's  really recommended.

At this time, new detectors MTN6303-XXXX also have native constant regulation working so well, more much better than use a MTN6308xx that native doesn't have this option.

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore