Hello,
Iam using IP backbone for lines and area with IP Router MTN6500-0103.
My question now how to add group address to IP Router filter table manual.
Link copied. Please paste this link to share this article on your social media post.
Hello!
As suggested by Heribert, ETS automatically creates filter tables based on the associations between the various devices in the project.
If Wiser/SpaceLYnk is present in your system, the advice is to simulate its presence using a Dummy, so that ETS continues to create filter tables automatically whenever necessary.
However, you can access the "manual" compilation from the Topology view, selecting the Property option from the side bar and then the Information tab
Link copied. Please paste this link to share this article on your social media post.
Hello
ETS5 and ETS6 do not allow to manually edit the filter table of a coupler or IP router (as far I know this was possible in older ETS versions.
Now you can achieve the same by inserting a dummy in your project and link the necessary group addresses to it. By that the IP router and coupler will add those group addresses to their filter table.
Link copied. Please paste this link to share this article on your social media post.
Hello!
As suggested by Heribert, ETS automatically creates filter tables based on the associations between the various devices in the project.
If Wiser/SpaceLYnk is present in your system, the advice is to simulate its presence using a Dummy, so that ETS continues to create filter tables automatically whenever necessary.
However, you can access the "manual" compilation from the Topology view, selecting the Property option from the side bar and then the Information tab
Link copied. Please paste this link to share this article on your social media post.
Thank you sir