Hi,
I Have KNX DALI Gateway MTN6725-0004 , 2 Channel Dali Gateway. I Updated It With Firmware update 0.2 Release 1 So Its Now DALI Tunable.
I Am Facing Problem When Electric Mains Power Goes Out And When Its Come Back My Lights Drivers Address Being Change ( Driver Did not Get Assign Address, It Get Different Address ) So I Have To Do Reconfigured Each And Every time.
Any One Has Faced Issue Like This ?
Kindly Guide How Resolve This Issue
Link copied. Please paste this link to share this article on your social media post.
Yes,
most often:
- bad product on line
- shortcircut on line
Link copied. Please paste this link to share this article on your social media post.
The DALI gateway does not perform any addressing process after an power outage. I would rather assume the ECGs are loosing their addresses due to the power cut. You might check the communication on the DALI line with the help of a DALI monitoring tool (like Tridonic masterCONFiGURATOR) connected with a DALI/USB interface and see if there is any re-addressing. The tool would also allow to check the addresses.
Link copied. Please paste this link to share this article on your social media post.
I agree, try reassigning address on DALI ECG. Then do power off/on of the ECG. Try again to see if they loose heir adress. Should fix most error