IP camera visualization with Chrome

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • IP camera visualization with Chrome
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
sesa356649_brid
Ensign sesa356649_brid Ensign
Ensign

Posted: ‎2017-01-03 07:49 AM . Last Modified: ‎2024-07-14 11:54 PM

0 Likes
5
948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-01-03 07:49 AM

IP camera visualization with Chrome

Hello,

IP camera visualization with Chrome, seen  print screen below,  Is this a known issue?

The same problem occurs with 7'' U.motion screen !

With firefox or safari, everything works properly

Does someone know how to solve this problem?

Printscreen1.png

Best Regards

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa356649_brid
Ensign sesa356649_brid Ensign
Ensign

Posted: ‎2017-02-15 02:56 AM

0 Likes
0
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-02-15 02:56 AM

Many thanks Thomas, Erwin,

Br

See Answer In Context

Reply
Replies 5
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2017-01-03 11:36 PM

0 Likes
4
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-01-03 11:36 PM

Hi Jean-Luc,

I quickly checked your topic on my HL and faced the same issue but it seems that you selected the wrong function within HL.

I am not a specialist within video-formats but it seems to me that this is only a picture-format *.cgi. (Computer Generated Imagery).

Solution:

1. Select a real video-path with the ending .mjpg like "http://192.168.0.120/mjpg/video.mjpg"

2. Select within the HL-Admin-Area the function "Frame" instead of "Camera". Because there you can select a "refresh-rate" in seconds

and than it is working as well (somehow because it is not a fluent video only an updated picture according to the configured "refresh-rate".

Kind regards

Thomas

Kind regards
Thomas

Application Design Engineer
Reply
sesa356649_brid
Ensign sesa356649_brid Ensign
Ensign

Posted: ‎2017-01-04 07:34 AM

0 Likes
3
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-01-04 07:34 AM

Hi Thomas,

Thanks for your help, sorry, yesterday I posted a wrong print screen, it seems that the 'Frame" trigger the camera view, seen prints screen below

the first point alone doesn't open the camera view , but when combining the both, view goes open ?

Why do this problem occur only with "Google chrome"  ?

Best  Regards

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2017-01-04 10:45 PM

0 Likes
2
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-01-04 10:45 PM

Hi Jean-Luc,

Sorry but I do not understand fully your answer?! Are you using the *.mjpg url within the frame? Please sent me your project so that I can see more in detail what is ongoing.

Kind regards

Thomas

Kind regards
Thomas

Application Design Engineer
Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2017-01-05 05:41 PM

0 Likes
1
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-01-05 05:41 PM

Camera frame is a img container.

By default a img container does not support basic authentication.

Only way to solve this is to create a widget with a iframe.

The result will look almost the same and with some extra css you can make it look identical.

Another option is to make a hidden page with iframe, when this is loaded the authentication is not needed anymore for the camera img object.

BR,

Erwin van der Zwart

Reply
sesa356649_brid
Ensign sesa356649_brid Ensign
Ensign

Posted: ‎2017-02-15 02:56 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-02-15 02:56 AM

Many thanks Thomas, Erwin,

Br

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore