IP Address not found in Wiser for KNX

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • IP Address not found in Wiser for KNX
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
Samimul_Islam
Lieutenant JG Samimul_Islam
Lieutenant JG

Posted: ‎2023-12-18 02:00 AM . Last Modified: ‎2024-07-14 11:41 PM

0 Likes
7
3404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-18 02:00 AM

IP Address not found in Wiser for KNX

Hello

Please be informed that when we change the IP address in LSS100100 where we have not found the IP address. we are trying advance IP scanner and others software but failed which hardware version is V3.1, RN-2019-W17-0978 is not found IP address.

Also, we have another issue LSS100100 which configuration and button on/off ok but actuator not functional that means light not work on/off state.

we are awaiting for your positive replay to solve the issue. 

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • Wiser for KNX
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-01-02 05:17 AM

0 Likes
0
3380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-02 05:17 AM

Hello Samimul,

 

to "if i purchase 16GB or 32GB card it will be ok, or not?"
Tests done with up to 8GB. So I guess higher sizes could work also.

to "Part-2: Please see the another video for switch actuator not work when we pressed button in W4KNX (LSS100100)"
I checked your ETS-Project and either you sent to me a wrong one (early version or backup) but the switch-actuator has no GA's linked to the dedicated objects?!
And it seems that your latest configuration was not downloaded yet.
ETS-ViewETS-View

 

Related to the provided W4K-Backup ... I was not able to open it. Which FW-Version you are using?
Did you gave a PW?
2024-01-02_13h55_48.png

 

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Reply
Replies 7
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2023-12-19 01:17 AM . Last Modified: ‎2023-12-19 01:17 AM

0 Likes
0
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-19 01:17 AM

For the IP issue, you might have entered incorrect details, to access the controller again you can boot the device in temporary settings as stated in the manual.

temporary settings default ip.jpg

For the feedback issue, when a device is not sending a feedback you might concider to use the main object as feedback object otherwise the system does not know the actual state..

main object.jpg

 

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2023-12-19 01:26 AM

0 Likes
1
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-19 01:26 AM

Hi Samimul,

 

I would like to divide your post into two parts.


Part1, you changed the IP-Address and now you cant find the device anymore.
With the procedure below you can go back to default IP-Settings (192.168.0.10) without changing anything within the general configuration of all your scripts, Visu, logics etc..

 

Default-IP-SettingsDefault-IP-Settings

Please try it and let me know.

 

Part2, you have created in a Visu a light switch which is properly working within LSS100100 but finally the KNX-Actuator does not react.
It would be very helpful to get more detailed information on this topic as it is otherwise pretty difficult to help you out. Please provide dedicated pictures of the configuration or even a video to better understand what you have done.

 

Kind regards
Thomas

Application Design Engineer
Reply
Samimul_Islam
Lieutenant JG Samimul_Islam
Lieutenant JG

Posted: ‎2023-12-28 06:24 PM

0 Likes
0
3387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-28 06:24 PM

Hi,
Sorry for late replay. we have tested different way to solve the issue but we have failed.
For Part-1: As per your instruction, we have tried to reset Temporary setting of W4KNX (LSS100100) where LED1 is blinding and LED2 is totally off what's why i have not reset it. Please see the attached video for your understanding.
Part-2: Please see the another video for switch actuator not work when we pressed button in W4KNX (LSS100100)
Note: our 3 devices not work still now . please help us how to solve it. Please see the following link

 

https://drive.google.com/drive/folders/1Kez0Xru1n6TqI1Hj2CMd7rCRQ4e05msw?usp=sharing

 

Best Regards

Samimul Islam

 

Attachments
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2023-12-29 01:30 AM

0 Likes
1
3386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-29 01:30 AM

Hello Samimul,

 

Part1: I am very sorry but for me it is not fully clear if you performed the reset, to reach the temporary IP-Settings, or not.
Out of the video I can just see the status described from you but no further information if you are able now to reach the device (IP-Point of view) or not as a first step.
Out of the video I could also identify the production date (W17/2019) ... so I guess it is not a new device which you bought recently?! Why I am saying that ... if the device is still within warranty period then you can exchange the device. In case warranty period is over ... we could try to flash the memory card. I can provide dedicated material (Image/HowTo).
Pre condition for that is that you feel comfortable with this steps to perform.

 

Part2:
Out of the video I can see blinking error LED of the actuator. So not sure if the actuator is working properly in general. Does the actuator works properly when you sent dedicated telegramms with the help of the ETS?
Can you please share the ETS-Project and a Backup of your W4K please?

In general ... it would be helpful to get for both cases also the dedicated Firmware-Version you use on the devices.

 

 

Kind regards
Thomas

Application Design Engineer
Reply
Samimul_Islam
Lieutenant JG Samimul_Islam
Lieutenant JG

Posted: ‎2023-12-30 07:49 PM

0 Likes
0
3384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-30 07:49 PM

Hello Thomas

Thank you for your continuous support. 

Part-1: I have reset it but can not found temporary IP which LED-2 totally off so that i am unable understand it is perfectly reset or not . I have tried which your provided with color mark yellow. Can you provided necessary document for flash the memory card, which inside W4KNX is 1GB, running market may not found 1 GB Card, if i purchase 16GB or 32GB card it will be ok, or not?

Part-2: please find the following link for your better understanding.

https://drive.google.com/drive/folders/1Kez0Xru1n6TqI1Hj2CMd7rCRQ4e05msw?usp=sharing

 

Regards

Samimul Islam

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-01-02 01:00 AM

0 Likes
1
3381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-02 01:00 AM

Hello Samimul, 
please find with the attached link the dedicated material.

https://schneiderelectric-my.sharepoint.com/:f:/r/personal/sesa79854_se_com/Documents/Sharefolder/LS... 

 

 

Kind regards
Thomas

Application Design Engineer
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-01-02 05:17 AM

0 Likes
0
3381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-02 05:17 AM

Hello Samimul,

 

to "if i purchase 16GB or 32GB card it will be ok, or not?"
Tests done with up to 8GB. So I guess higher sizes could work also.

to "Part-2: Please see the another video for switch actuator not work when we pressed button in W4KNX (LSS100100)"
I checked your ETS-Project and either you sent to me a wrong one (early version or backup) but the switch-actuator has no GA's linked to the dedicated objects?!
And it seems that your latest configuration was not downloaded yet.
ETS-ViewETS-View

 

Related to the provided W4K-Backup ... I was not able to open it. Which FW-Version you are using?
Did you gave a PW?
2024-01-02_13h55_48.png

 

Kind regards
Thomas

Application Design Engineer
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore