Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello, when setting DALI KNX product protected by password different than defaut admin/admin. The app in SL/HL don't work. We don't have field to enter user/password...
Link copied. Please paste this link to share this article on your social media post.
DALI application is now capable to handle MTN6725-0001 - KNX DALI gateway (fw 1.xx & fw 3.xx)
https://community.se.com/t5/KNX-Forum/DALI-application-20200227-available/m-p/190789#M902
Link copied. Please paste this link to share this article on your social media post.
Nothing heard in this direction yet. I will check it and come back.
Link copied. Please paste this link to share this article on your social media post.
In ETS, when you change mtn6725-0001 password, you don't have field in DALI App of SL/HL to fill the new password
Link copied. Please paste this link to share this article on your social media post.
Thanks a lot for the hint!
Link copied. Please paste this link to share this article on your social media post.
Hello,
The DALI application available in version 20190115 on marketplace is not compatible with KNX DALI gateway (MTN6725-0001) running on firmware 3.x_x. There were made some changes in the DALI gateway's API which we use in our DALI application.
The problem is not in credentials. Credentials are not part of http commands used in DALI application.
We have fixed the DALI application in a way to be compatible with older firmware 1.x_x and 3.1_x both. Updated DALI application is going to be tested and release on marketplace.
Link copied. Please paste this link to share this article on your social media post.
DALI application is now capable to handle MTN6725-0001 - KNX DALI gateway (fw 1.xx & fw 3.xx)
https://community.se.com/t5/KNX-Forum/DALI-application-20200227-available/m-p/190789#M902
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.