I have found a problem in the HomeLYnk when using the trend logger with counter values.
The data from "today" is marked as "yesterday" in the trends when viewing the data. I expect that this happens because the summations is made at midnight and therefore timestamped with the day after.
I have attached two pictures to show what I mean. As you can see on one picture, the total sum of Nov 18 is 3.2kWh but this is logged as Nov 19 on the "monthly" picture.
Does anyone have a solution to this?
//Michael
Michael Johansen
Solution Architect
M +4528991535
E michael.johansen@se.com
LinkedIn https://www.linkedin.com/in/mich4el/
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Michael,
This is a know item and should be fixed in FW 1.4.
BR,
Erwin
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Erwin
Thanks for the response. Is there an estimated time for the new firmware and will it fix the already logged values?
BR, Michael
Michael Johansen
Solution Architect
M +4528991535
E michael.johansen@se.com
LinkedIn https://www.linkedin.com/in/mich4el/
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Michael
Some time in February and yes it will fix old trends. There will be new trend engine and old trends will be converted to new one during upgrade. We will also have lower sampling rate.
Regards
Daniel
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Daniel
Thanks! That sounds great. Will we also get an easy way to export the data from the trends to some external system. E.g. if a customer have used the HomeLYnk/SpaceLYnk as a small energy server but wants to migrate to PME?
Kind regards, Michael
Michael Johansen
Solution Architect
M +4528991535
E michael.johansen@se.com
LinkedIn https://www.linkedin.com/in/mich4el/
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
This you can do already by scripts but in new fw we will need new script as data will be stored in different place. In new FW there will be new possibility we integrated cloud connector and via cloud we can export data to 3rt party as csv. For now this will be available in France but other countries can join on request.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hej Daniel
Can you share a template script for this with me?
Best regards, Michael
Michael Johansen
Solution Architect
M +4528991535
E michael.johansen@se.com
LinkedIn https://www.linkedin.com/in/mich4el/
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Michael,
Use this for reading trends with script and export to CSV on internal FTP server: You need to enable the server first and check credentials and IP address in the scrip (default ftp:ftp)
require('socket.ftp')
require('genohm-scada.trends')
-- ftp file
ftpfile = string.format('ftp://ftp:ftp@192.168.10.200/' .. 'All trends last month data export' .. '_%s.csv', os.date('%Y-%m-%d_%H-%M', timestamp))
-- csv buffer
buffer = {}
-- Get all trend names from DB
trends_table = db:getall('SELECT name FROM trends ORDER BY name DESC')
for _, trend_names in ipairs(trends_table) do
-- Get current timestamp
timestamp = os.time()
now = os.date('*t', timestamp)
trend_name = trend_names.name
-- Get last month for data and determine number of days in this month
trenddatamonth = trends.fetch(trend_name, 'month', now)
-- Add to buffer
table.insert(buffer, '"Average usage a month (' .. trend_name .. ')"')
-- Add empty line
table.insert(buffer, '""')
-- Add header
table.insert(buffer, trend_name .. ',"Day","Average day value"')
for _, row in ipairs(trenddatamonth) do
-- format csv row
csv = string.format('%q,%q,%q', "", "" .. string.format("%02d", row[1]) .. "-" .. string.format("%02d", now.month) .. "-" .. now.year, row[2])
-- add to buffer
table.insert(buffer, csv)
end
-- Add empty line
table.insert(buffer, '""')
table.insert(buffer, '"Average usage a day (' .. trend_name .. ')"')
-- Add empty line
table.insert(buffer, '""')
for i = 1, now.day, 1 do
now.day = i
average_value = 0
trenddata = trends.fetch(trend_name, 'day', now)
-- Add header
table.insert(buffer, trend_name .. ',' .. string.format("%02d", i) .. '-' .. string.format("%02d", now.month) .. '-' .. now.year .. ',"Average hour value"')
for _, row in ipairs(trenddata) do
-- format csv row
csv = string.format('%q,%q,%q', "", "" .. string.format("%02d", (row[1]-1)) .. ":00:00", row[2])
-- add to buffer
table.insert(buffer, csv)
average_value = average_value + row[2]
end
-- Add empty line
table.insert(buffer, "")
-- add to buffer
table.insert(buffer, "Average value month (" .. string.format("%02d", now.month) .. "-" .. now.year .. ")," .. trenddatamonth[i][2])
-- Add empty line
table.insert(buffer, "")
end
end
-- upload to ftp only when there's data in buffer
if #buffer > 1 then
result, err = socket.ftp.put(ftpfile, table.concat(buffer, '\r\n'))
-- error while uploading
if err then
alert('FTP upload error: %s', tostring(err))
end
else
log('No data found inside trend ' .. trend_name)
end
Good luck (:
BR,
Erwin van der Zwart
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Michael,
Use this script to read and export a single trend :
require('socket.ftp')
require('genohm-scada.trends')
trend_name = 'Your trend name to export'
-- Get current timestamp
timestamp = os.time()
now = os.date('*t', timestamp)
-- ftp file
ftpfile = string.format('ftp://ftp:ftp@192.168.10.200/' .. trend_name .. '_%s.csv', os.date('%Y-%m-%d_%H-%M', timestamp))
-- Get last month for data and determine number of days in this month
trenddatamonth = trends.fetch(trend_name, 'month', now)
log(trenddatamonth)
-- csv buffer
buffer = { '"Average usage a month"' }
-- Add empty line
table.insert(buffer, '""')
-- Add header
table.insert(buffer, trend_name .. ',"Day","Average day value"')
for _, row in ipairs(trenddatamonth) do
-- format csv row
csv = string.format('%q,%q,%q', "", "" .. string.format("%02d", row[1]) .. "-" .. string.format("%02d", now.month) .. "-" .. now.year, row[2])
-- add to buffer
table.insert(buffer, csv)
end
-- Add empty line
table.insert(buffer, '""')
table.insert(buffer, '"Average usage a day"')
-- Add empty line
table.insert(buffer, '""')
for i = 1, now.day, 1 do
now.day = i
average_value = 0
trenddata = trends.fetch(trend_name, 'day', now)
-- Add header
table.insert(buffer, trend_name .. ',' .. string.format("%02d", i) .. '-' .. string.format("%02d", now.month) .. '-' .. now.year .. ',"Average hour value"')
for _, row in ipairs(trenddata) do
-- format csv row
csv = string.format('%q,%q,%q', "", "" .. string.format("%02d", (row[1]-1)) .. ":00:00", row[2])
-- add to buffer
table.insert(buffer, csv)
average_value = average_value + row[2]
end
-- Add empty line
table.insert(buffer, "")
-- add to buffer
table.insert(buffer, "Average value month (" .. string.format("%02d", now.month) .. "-" .. now.year .. ")," .. trenddatamonth[i][2])
-- Add empty line
table.insert(buffer, "")
end
-- upload to ftp only when there's data in buffer
if #buffer > 1 then
result, err = socket.ftp.put(ftpfile, table.concat(buffer, '\r\n'))
-- error while uploading
if err then
alert('FTP upload error: %s', tostring(err))
end
else
log('No data found inside trend ' .. trend_name)
end
BR,
Erwin van der Zwart
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Erwin
That's awesome! Thanks a lot! I will try it later this week (:
BR, Michael
Michael Johansen
Solution Architect
M +4528991535
E michael.johansen@se.com
LinkedIn https://www.linkedin.com/in/mich4el/