Hi team
Need help me on MTN6354-0019 high bay sensor programming.
Problem- In one of the Wearhouse we installed this sensor, if we use one sensor for one circuit then this is working fine , asper site req, we used 3 sensors for one circuit because no of light fixtures are more. Given the time delay of 3min, in this case once we gave the movement the load is getting on/off, on/off. its not working properly, some times not taking the movement also. what could be the problem and also need solution.
Is we can configure master /slave configuration in ETS. If yes pls attach the documents ?
Waiting for your valuable replay.
Link copied. Please paste this link to share this article on your social media post.
Hello TECHMECH,
to "Is we can configure master /slave configuration in ETS. If yes pls attach the documents ?"
The master/slave function is pretty easy to handle.
Within a dedicated Light-Channel you find a parameter called "Slave input".
With this paramter you can define how the master/slave function works.
Selection "Slave input = ON"
Each ON-Value on the slave input will start/retrigger the staircase timer, if the brightness condition is fulfilled.
An ON-Value is the same as a movement detected in front of the detector.
This is the normal function when having other detectors as slaves and it is the same function as the master-trigger object of the Argus.
Selection "Slave input = ON/OFF"
With the slave input set to ON/OFF, then as long as the slave input is ON the staircase timer is permanently retriggered.
Not until the slave input is OFF and there is no movement in front of the detector, the staircase timer will run out.
For example to keep the light on without movement using a time switch or push-button, but still brightness dependent.
Link copied. Please paste this link to share this article on your social media post.
Hello TECHMECH,
to "Is we can configure master /slave configuration in ETS. If yes pls attach the documents ?"
The master/slave function is pretty easy to handle.
Within a dedicated Light-Channel you find a parameter called "Slave input".
With this paramter you can define how the master/slave function works.
Selection "Slave input = ON"
Each ON-Value on the slave input will start/retrigger the staircase timer, if the brightness condition is fulfilled.
An ON-Value is the same as a movement detected in front of the detector.
This is the normal function when having other detectors as slaves and it is the same function as the master-trigger object of the Argus.
Selection "Slave input = ON/OFF"
With the slave input set to ON/OFF, then as long as the slave input is ON the staircase timer is permanently retriggered.
Not until the slave input is OFF and there is no movement in front of the detector, the staircase timer will run out.
For example to keep the light on without movement using a time switch or push-button, but still brightness dependent.