Dynamic control of EVlink via Homelynk

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Dynamic control of EVlink via Homelynk
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic KNX Forum
Start a Topic
sesa333683_brid
sesa333683_brid Cadet
Cadet

Posted: ‎2018-02-07 12:30 PM . Last Modified: ‎2024-07-14 11:50 PM

0 Likes
4
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-02-07 12:30 PM

Dynamic control of EVlink via Homelynk

I'm looking for a logical program for Homelynk to dynamically control/limit the EV link Wallbox G4 or EV link parking in function of the current that is still available in an installation (ie. value of iEM3155 for example).

Can anybody help? Much appreciated!

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Tags (5)
  • Tags:
  • current
  • dynamic
  • evlink
  • homelynk
  • iem3155
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2018-02-08 09:30 AM

0 Likes
3
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-02-08 09:30 AM

Hello Simon,

as quickly checked by phone ... you will find attached the document which goes in the direction you are looking for.

Please check it out and let me know if this is that what you are looking for. Again, sorry for the German document but
due to the fact that you are able to read German you can justify if it is valueable for you or not.

If yes than I will organize the dedicated project-backup too.

Kind regards

Thomas

Kind regards
Thomas

Application Design Engineer
Attachments
Reply
sesa333683_brid
sesa333683_brid Cadet
Cadet

Posted: ‎2018-02-09 12:09 AM

0 Likes
2
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-02-09 12:09 AM

Hi Thomas,

This looks exactly like what I was looking for!
Can you please send the project-backup?

Thanks a lot!

Best regards,

Simon

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2018-02-09 12:20 AM

3 Likes
1
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-02-09 12:20 AM

Hi Simon,

attached you will a version for 4 charging points, which runs at a customer in Cologne, he has 4 E-Passats as a company car for city traffic. HomeLYnk has SW 1.5.1.

The application also contains the trends for the currents in the three phases of the building supply and for the sum of the charging currents of the EVlink in the three phases (see .doc)

Often there are questions about the billing of the loading processes. In this project an EVlink export function is used (no function in the homeLYnk application)

The customer exports the report of the loading processes from the EVlink via csv and evaluates it for billing in Excel (see xls).

He knows that

-when,

-who,

-at which charging point,

-What charging energy

was consumed.

Of course it will be again a German lesson

Kind regards

Thomas

Kind regards
Thomas

Application Design Engineer
Attachments
EVlink Lademanagement 4 Ladepunkte 1 Zähler V65 ULIP.tar.gz
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2018-03-21 11:39 PM

1 Like
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-21 11:39 PM

Hi Simon,

is this topic answered/solved? If "Yes" please mark it accordingly.

Kind regards
Thomas

Kind regards
Thomas

Application Design Engineer
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore