Hello,
Do our DALI gateways MTN6725-0001 have a maximum number of group addreses you can link?
Kind regards,
Hannes
Link copied. Please paste this link to share this article on your social media post.
The DALI Gateway is a System B device.
It means it can manage up to 65.536 Group Object and therefore 65.536 Group addresses (1 each group object).
You can even think to connect several group addresses to the same group object.
Even in this case, the total amount of group addresses is 65.536.
Personally, I didn't reach this limit, but with a small test, I've linkek without any problem 1024 group addresses (1bit) to the same group object.
Be patient, because ETS (ETS5 in my case) takes time to complete the task. 😉
Link copied. Please paste this link to share this article on your social media post.
Thank you Cristiano !