Do our DALI gateways MTN6725-0001 have a maximum number of group addreses you can link?
Kind regards,
Hannes
  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
View products (3)
Cristiano_Carli_Ballola
Lt. Commander Cristiano_Carli_Ballola Lt. Commander
Lt. Commander
Posted: ‎2015-04-21 02:32 AM
1
568
The DALI Gateway is a System B device.
It means it can manage up to 65.536 Group Object and therefore 65.536 Group addresses (1 each group object).
You can even think to connect several group addresses to the same group object.
Even in this case, the total amount of group addresses is 65.536.
Personally, I didn't reach this limit, but with a small test, I've linkek without any problem 1024 group addresses (1bit) to the same group object.