With renewing my KNX installation and programming it in ETS6.
All my Merten KNX Argus 180UP (632660) are giving below error message.
Similar I have issues with my Merten KNX Argus Presence Basic 630719 and other Merten PIR sensors.
Searching the internet and downloading/testing al versions of application software, do not solve the issue.
Someone an idea?
- Labels:
-
SpaceLogic devices
-
Wiser for KNX
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thanks for extensive reply.
I had already created a new project to test the components separately from my installation.
Also in this project I got the same error message.
ETS6 is in compatibility mode.
Meanwhile, I found the original Merten application files.
With this it works again, with the SE files the error file as shown in my original post.
Anyhow, it's solved with the original Merten files (for both indicated sensors)
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Timme
Error message indicates problem with fastdownload plug-in.
632660 and 630719 are using a (hidden) plug-in for faster download. To allow the plug-in to run ETS must run in compatiblity mode. In ETS6 compatibility mode can be activated in section settings/presentation/project editing. Please double-check if ETS is in compatibility mode.
If the project was imported the plug-in will not be installed during the import of the project. To install the plug-in please create a new ETS project and insert 632660 or 630719. This procedure will then install the plug-in. Afterwards the plug-in can also be used in your main project.
Best regards
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thanks for extensive reply.
I had already created a new project to test the components separately from my installation.
Also in this project I got the same error message.
ETS6 is in compatibility mode.
Meanwhile, I found the original Merten application files.
With this it works again, with the SE files the error file as shown in my original post.
Anyhow, it's solved with the original Merten files (for both indicated sensors)
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
For products with plug-in it makes a difference if it is SE or Merten brand because for each brand the plug-in is registered separately in ETS and the plug-in file is stored in different location on your computer. That's why I wrote to create new project with 632660 or 630719 (and not MTN632660 or MTN630719).
Just to make you understand why it is working now.