Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

SpaceLogic C-Bus Controllers NEW Firmware Update (V.1.18.0)

SpaceLogic C-Bus Forum

Schneider Electric forum about the C-Bus platform to get support and share knowledge including Network Automation Controller (NAC), Application Controller (AC) at selection, installation and troubleshooting sides.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic C-Bus Forum
  • SpaceLogic C-Bus Controllers NEW Firmware Update (V.1.18.0)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sesa96364
sesa96364 Schneider Alumni (Retired)
9
KCWong
Lieutenant KCWong Lieutenant
4
DarrenMullighan
Ensign DarrenMullighan Ensign
1
SJFP
Lieutenant | EcoXpert Master SJFP Lieutenant | EcoXpert Master
1
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic C-Bus Forum
Start a Topic
Asli
Ensign Asli Ensign
Ensign

Posted: ‎2024-09-06 02:05 AM

1 Like
1
894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-06 02:05 AM

SpaceLogic C-Bus Controllers NEW Firmware Update (V.1.18.0)

Dear SpaceLogic C-Bus Community,
We're pleased to announce that the new firmware (version 1.18.0) for SpaceLogic C-Bus Controllers is now available for download from se.com. 
You can find the related zip files under the "se.com Software and Firmware" page for C-Bus (link provided here). 
The new firmware version V1.18.0 is compatible with 5500NAC2, 5500AC2, 5500NAC, 5500SHAC, LSS5500NAC, and LSS5500SHAC.
 
The main update in this new firmware release (V1.18.0) includes:
  • Bug fixes:
    • Fixed the customer's issue regarding the incorrect transfer of Error object values exported to the BACnet client.
    • Resolved issues related to the incorrect behaviour of the ramp off to level when the indicators ramp on correctly.
Note:      There are no updates in the User Manual with this firmware update.
 
Sincerely,
C-Bus Team
Labels
  • Labels:
  • C-Bus Controllers
  • Controllers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Benny_A
Crewman Benny_A
Crewman

Posted: ‎2025-05-21 12:24 AM

0 Likes
0
427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-21 12:24 AM

HI There the link provided dose not work for me jest takes me to a blank page?

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore