Network Bridge Not Passing Commands

SpaceLogic C-Bus Forum

Schneider Electric forum about the C-Bus platform to get support and share knowledge including Network Automation Controller (NAC), Application Controller (AC) at selection, installation and troubleshooting sides.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic C-Bus Forum
  • Network Bridge Not Passing Commands
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sesa96364
sesa96364 Schneider Alumni (Retired)
9
KCWong
Lieutenant KCWong Lieutenant
4
ZeeZee97
Administrator ZeeZee97 Administrator
1
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic C-Bus Forum
Start a Topic
MarkHenry
Lieutenant | EcoXpert Master MarkHenry Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-07-14 09:56 PM

0 Likes
6
2503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-14 09:56 PM

Network Bridge Not Passing Commands

Have recently been running into the same issue on various site with using 5500NB.

Bridges just stop passing commands to the adjacent network. These sites are all < 1 year.

When connecting to the network, Toolkit has the ability to communicate through the bridge to the other network.

Scans as normal but when logging commands on diagnostic utility they are not being passed through.

Opening the bridge from the network, the GUI it shows that the send to adjacent network enabled.

Power cycle doesn't rectify but by un-ticking send to adjacent network then saving and then re-tick and save.

Once that done unit then bridge starts operating as expected.

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DarrenMullighan
Ensign DarrenMullighan Ensign
Ensign

Posted: ‎2022-07-31 08:07 PM

0 Likes
0
2491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-31 08:07 PM

Hi Mark,

 

Apologies for the delay, I have been off work for the past 3 weeks.

 

Based off your assessment of the bridge, my initial thoughts are that there is something wrong with the internals of the unit.

 

It is odd to me that you can scan the adjacent network over the bridge (assuming reliably and that the data comes through in a consistent manner), but that commands do not traverse the bridge over a longer period of time after reenabling the send commands to adjacent network option.

 

Whats the period of time roughly before the bridges fail to transfer commands?

Tags (1)
  • Tags:
  • english
Reply
sesa59140_bridg
sesa59140_bridg Cadet
Cadet

Posted: ‎2022-08-01 04:50 PM

0 Likes
1
2487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-01 04:50 PM

Hi Mark,

 

In addition to Darren's reply, Does the NB continue to work properly after your re-programme sequence or does it fail again?

Cheers

Steve Dunn

Tags (1)
  • Tags:
  • english
Reply
sesa59140_bridg
sesa59140_bridg Cadet
Cadet

Posted: ‎2022-08-01 04:53 PM

0 Likes
2
2485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-01 04:53 PM

Hi Mark,

Another thought, Does this Bridge return to bad behavior after a Power cycle?

Cheers

Steve Dunn

 

Tags (1)
  • Tags:
  • english
Reply
MarkHenry
Lieutenant | EcoXpert Master MarkHenry Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-08-01 05:00 PM

0 Likes
0
2484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-01 05:00 PM

Hi Darren & Steve,

 

This issue has occurred at multiple sites. The bridge continues to operate for months normally and then stops after re-ticking the send to adjacent network. One one site it happened 3 times. We have replaced this bridge now.

When failed we are able to open the network through the bridge correctly and scan, only the bridge doesn't pass commands onto the other network. Toolkit shows that the send to adjacent network is ticked when opening from the network.

 

 

 

 

Tags (1)
  • Tags:
  • english
Reply
MarkHenry
Lieutenant | EcoXpert Master MarkHenry Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-08-01 05:03 PM

0 Likes
1
2482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-01 05:03 PM

Hi Steve,

 

once re-ticked, the unit works correctly after restore from a power cycle. Disconnected both sides of the bridge to power cycle to confirm operation.

Tags (1)
  • Tags:
  • english
Reply
PeterLags
Lieutenant JG PeterLags Lieutenant JG
Lieutenant JG

Posted: ‎2022-08-01 05:20 PM . Last Modified: ‎2022-08-01 05:22 PM

0 Likes
0
2478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-01 05:20 PM

is local SAL enabled on the device you are connecting to the network and all PCI type devices? inc NAC/SHAC, Device Formally known as WISER, enabled devices, CNI, PCI ....

 

if any device has this disabled it causes bridges to stop passing commands originating from that device as the bridge believes the cmd has already passed through one network.

 

toolkit originated commands will still work however as they are directed commands with the network routing included

- I believe you need the diagnostic utility to check and enable this

 

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore