Posted: 2021-07-12 05:16 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Team,
We are looking a Lua Script for NAC/SHAC for Daikin VRV Air Condition System Operation via Modbus RTU.
Kindly share the asked script.
Thanks,
Digital Technologies.
Link copied. Please paste this link to share this article on your social media post.
Hi,
You would require a JSON file for modbus integration. (Modbus tcp or modbusRTU would both use the same json file)
Sorry to say I am not aware of a JSON for this ( if there is a JSON it probably is not "tested and validated" on a live system).
I think from looking at some Daikin Specification docs that is is quite complicated as it requires supporting alot of bitmasking values.
The Docs suggest that 1 card is used for up to 16 units.