Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Vw3A1111 connected to ATV320 fail TTC

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • Vw3A1111 connected to ATV320 fail TTC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
15
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Start a Topic
Solved
Jerry.Chen
Crewman Jerry.Chen
Crewman

Posted: ‎2023-08-31 07:49 PM . Last Modified: ‎2023-08-31 07:50 PM

1 Like
2
1444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-31 07:49 PM . Last Modified: ‎2023-08-31 07:50 PM

Vw3A1111 connected to ATV320 fail TTC

JerryChen_1-1693536418920.png

TTC error after connecting ATV320 V2.9 IE34

Labels
  • Labels:
  • Drives & Motor Control
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ahmed_Alzafer
Lieutenant JG Ahmed_Alzafer Lieutenant JG
Lieutenant JG

Posted: ‎2023-09-11 08:04 AM

0 Likes
0
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-11 08:04 AM

hello Jerry 

 

Both the ATV320 VFD and the VW3A1111 keypad firmwares have been upgraded to support compatibility. (6-2019)

Firmware versions required:
ATV320  V2.9IE37#3
VW3A1111  V2.0IE53
Earlier versions are not compatible. 

Note: Early versions of the ATV320 catalog included the VW3A1111 keypad by mistake, but was removed from the Sept 2018 catalog.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Jean_Commeignes
Administrator Jean_Commeignes Administrator
Administrator

Posted: ‎2023-09-06 02:09 AM

1 Like
0
1401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-06 02:09 AM

@Zirwa , Could any Vw3A1111 or ATV320 expert adress this issue?

Jean COMMEIGNES
Schneider Electric Community Manager for Power & Building
Reply

Link copied. Please paste this link to share this article on your social media post.

Ahmed_Alzafer
Lieutenant JG Ahmed_Alzafer Lieutenant JG
Lieutenant JG

Posted: ‎2023-09-11 08:04 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-11 08:04 AM

hello Jerry 

 

Both the ATV320 VFD and the VW3A1111 keypad firmwares have been upgraded to support compatibility. (6-2019)

Firmware versions required:
ATV320  V2.9IE37#3
VW3A1111  V2.0IE53
Earlier versions are not compatible. 

Note: Early versions of the ATV320 catalog included the VW3A1111 keypad by mistake, but was removed from the Sept 2018 catalog.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore