How to avoid condensation problems in my drive installation

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • How to avoid condensation problems in my drive installation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
14
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
11
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Start a Topic
Solved
AlexandreBoulet
Administrator AlexandreBoulet Administrator
Administrator

Posted: ‎2021-03-26 12:07 AM . Last Modified: ‎2021-03-26 12:56 AM

3 Likes
3
2713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-26 12:07 AM . Last Modified: ‎2021-03-26 12:56 AM

How to avoid condensation problems in my drive installation

Hello, I need to design a drive installation for a sugar mill located in a tropical environment similar to the one pictured. There the  customer is facing quite high humidity levels and temperature differences between day / night. Has someone experience with VSD´s in such environments? Thanks

Alexandre Boulet
Schneider Electric - Exchange Launch Leader
Labels
  • Labels:
  • Design & Build
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2021-03-26 03:08 AM

5 Likes
0
2700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-26 03:08 AM

The change of temperature in a cabinet can create some condensation on the components of the cabinet.

It appears generally just after power on a cabinet, all components / products are cold and get higher in temperature, this difference can create condensation...  

Different solutions will help to reduce or solve this kind of phenomena.

It is possible to let the concerned product always connected on the main, this allows to keep inside product a stable temperature and then avoid possible condensation. This will avoid possible condensation inside the product only.

Another possibility to help reducing condensation is to install a small heater inside the cabinet (preferable possible with a thermal setting), then it will allow a stable temperature in all cabinet and then avoiding this phenomena for all components of the cabinet...

the thermal setting will allow an adjustment of temperature and then avoid energy consumption when it is not necessary.

Bruno Jacqz, Drives training leader

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2021-03-26 03:08 AM

5 Likes
0
2701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-26 03:08 AM

The change of temperature in a cabinet can create some condensation on the components of the cabinet.

It appears generally just after power on a cabinet, all components / products are cold and get higher in temperature, this difference can create condensation...  

Different solutions will help to reduce or solve this kind of phenomena.

It is possible to let the concerned product always connected on the main, this allows to keep inside product a stable temperature and then avoid possible condensation. This will avoid possible condensation inside the product only.

Another possibility to help reducing condensation is to install a small heater inside the cabinet (preferable possible with a thermal setting), then it will allow a stable temperature in all cabinet and then avoiding this phenomena for all components of the cabinet...

the thermal setting will allow an adjustment of temperature and then avoid energy consumption when it is not necessary.

Bruno Jacqz, Drives training leader
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ReinhardK
Ensign ReinhardK Ensign
Ensign

Posted: ‎2021-04-01 08:10 AM

3 Likes
0
2666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-01 08:10 AM

Condensation appears when air is cooled down lower than its dew point, which depends on the relative humidity and air pressure.
Look for a h-x diagram or calculator on the web to figure out this critical temperature.

On electrical installations, it´s critical when the cubical inside temperature is lower than on outside temperature, or the cooling air temperature.
To avoid problems hold the inner temperature higher than on the outside, this can be done by installing space heaters.
When AC units are used, make sure to set the cooling temperature not lower than the dew point.
Special cautions are necessary on liquid-cooled drive installations, follow here the guides in the corresponding ATV manuals. 

  • Tags:
  • condensation
  • english
  • liquid cooled
  • space heater
  • water cooled
Reply

Link copied. Please paste this link to share this article on your social media post.

MitchS
Crewman MitchS Crewman
Crewman

Posted: ‎2021-04-14 08:35 AM

1 Like
0
2607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-14 08:35 AM

To add to the other comments:

For new enclosed drives being quoted, some options are available such as VW3AP0501 enclosure heating and VW3AP2101 for motor heating (motors can get condensation in them as well as the cabinets).

For existing installations, SE has the ClimaSys™ Thermal Management System to help with heating, cooling, and monitoring enclosures of all types along with the software to monitor and inform decisions on everything.


01001000 01101001 00100001
There are 10 types of people in the world. Those who understand BINARY, and those who don't.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore