Altivar atv71 forward direction

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • Altivar atv71 forward direction
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
15
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2022-07-29 01:21 AM

1 Like
2
1871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-29 01:21 AM

Altivar atv71 forward direction

The input pin for forward direction LI1 isn't working

Is it possible to program LI5 for forward direction instead of LI1

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2022-10-14 06:12 AM

1 Like
0
1753
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-14 06:12 AM

On ATV71, LI1 is always set to forward.

Other functions can be set to this LI1 acccording to the feature available "multi assignment".

May be you can check first that the LI1 is really activated. Have a look inside the I/O Map. As shown on linked picture

 

Check that the drive is on "rdy" before you switch on LI1, check that PWR is activated (power removal), this is a safety input avoiding motor to start in case this is not activated. For information, on new drive now, it is named Safe Torque Off (STO)

Bruno Jacqz, Drives training leader

See Answer In Context

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Kevin_McDonald
Ensign Kevin_McDonald Ensign
Ensign

Posted: ‎2022-12-05 05:23 AM

0 Likes
0
1627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-05 05:23 AM

LI1 is forward or run permissive.  

 

Check in the IO Map if LI1 is high or low.  If low and does not respond, confirm for 24VDC between 24V and COM.  If there is still no response, recommend to replace the control board.

 

If LI1 is stuck in high, you may be able to change to 3 wire control where LI1 is permissive and LI2 is run forward.  

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2022-10-14 06:12 AM

1 Like
0
1754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-14 06:12 AM

On ATV71, LI1 is always set to forward.

Other functions can be set to this LI1 acccording to the feature available "multi assignment".

May be you can check first that the LI1 is really activated. Have a look inside the I/O Map. As shown on linked picture

 

Check that the drive is on "rdy" before you switch on LI1, check that PWR is activated (power removal), this is a safety input avoiding motor to start in case this is not activated. For information, on new drive now, it is named Safe Torque Off (STO)

Bruno Jacqz, Drives training leader
Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Kevin_McDonald
Ensign Kevin_McDonald Ensign
Ensign

Posted: ‎2022-12-05 05:23 AM

0 Likes
0
1628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-05 05:23 AM

LI1 is forward or run permissive.  

 

Check in the IO Map if LI1 is high or low.  If low and does not respond, confirm for 24VDC between 24V and COM.  If there is still no response, recommend to replace the control board.

 

If LI1 is stuck in high, you may be able to change to 3 wire control where LI1 is permissive and LI2 is run forward.  

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.