ATV930 Speed Loop Optimization

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • ATV930 Speed Loop Optimization
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
15
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Start a Topic
Solved
Boris11
Boris11
Cadet

Posted: ‎2024-01-25 04:16 PM

0 Likes
8
2378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-25 04:16 PM

ATV930 Speed Loop Optimization

 

Hello everyone!

 

I kindly ask you to help me with Speed Loop Optimization for ATV930:

 

The PFC is working correctly, but I have a problem with motor speed fluctuation

around reference speed in FVC control mode (closed loop).

It is about 3-4 rpm @ 1500 rpm, but it leads to mechanical stress for gearbox

in my case. How to remove or decrease the motor speed fluctuation?

 

Best regards,

Boris Churkin

Labels
  • Labels:
  • Drives & Motor Control
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2024-08-22 02:46 AM

1 Like
0
2224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-22 02:46 AM

Speed loop gain settings are available in your product. I advise you to use SoMove software, you will then easily be able to see all the speed loop optimization settings.

BJacqz_0-1724319913978.png

SSL, SPG & SIT are the first settings I would propose to set, and you have much more, a test of moving one setting at a time will help you to find the good compromise...

Hope it helps

Bruno Jacqz, Drives training leader

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2024-08-22 02:46 AM

1 Like
0
2225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-22 02:46 AM

Speed loop gain settings are available in your product. I advise you to use SoMove software, you will then easily be able to see all the speed loop optimization settings.

BJacqz_0-1724319913978.png

SSL, SPG & SIT are the first settings I would propose to set, and you have much more, a test of moving one setting at a time will help you to find the good compromise...

Hope it helps

Bruno Jacqz, Drives training leader
Reply

Link copied. Please paste this link to share this article on your social media post.

Denys
Crewman Denys
Crewman

Posted: ‎2025-01-27 02:08 AM

0 Likes
1
1956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-27 02:08 AM

I have same issue with ALT930 for hoist application in a close loop operation. With 50Hz speed setpoint, the RPM is fluctuate around 5 RPM. When I reduce speed to 45Hz, it became stable. 
I'll try with the proposed solution by BJacqz 

Reply

Link copied. Please paste this link to share this article on your social media post.

Denys
Crewman Denys
Crewman

Posted: ‎2025-01-27 04:52 AM

In response to Denys
1 Like
0
1946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-27 04:52 AM

And it's working. I solve the problem with fluctuation.

It didn't appear on the smaller size motor like 160kW, also hoist. So default settings were enough. But for 250kW motor hoist, it was a problem with fluctuation. 
Now after reducing proportional SPG (from 40 to 10%) and increasing SIT (from 150ms to 2000ms) it working well. During the load test will check again. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Slayer90
Slayer90
Cadet

Posted: ‎2025-02-13 04:50 AM

0 Likes
2
1856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-13 04:50 AM

Hy guys, I have same problem with hoist application, motor power 132kw. With fix speed after ramp up the current star abnormaly fluctuation like a sine signal. If i set a mode svc V Instead Fvc all works fine. I checked all for motor encoder and switch to another drive but still works bad.. Any idea for the problem? I tried to change values for speed loop but Nothing change.

Thanks for help

Reply

Link copied. Please paste this link to share this article on your social media post.

Denys
Crewman Denys
Crewman

Posted: ‎2025-02-14 11:55 PM

In response to Slayer90
0 Likes
1
1804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-14 11:55 PM

Hello @Slayer90 ,
I am not professional drive commissioning engineer and also require a lot of support, but I had similar problem before, when in FVC (with encoder) there was a speed fluctuation and in SVC mode (without encoder) wasn't.
We also replace the inverter and the encoder and even put a temporary encoder cable (which by the way improve, but not solve the issue).
Solution in my case, was the encoder cable proper earthing, to prevent the cable magnetization. The trick was in earthing the encoder cable shield to the inverter body (Encoder cable shielding, ATV930 Installation manual) and to connect this shield to the encoder's earth terminal. Encoder (we use AB type) has 7 terminals, as power, neutral, A+/B+, A-/B- and one more for the earthing connection, where we connect the cable shield, which was earthed on the drive side only. 

After the proper connections the fluctuations helps.

 

And right now it come back after mechanical disassemble and assemble the hoist  gearbox. And in any mode FVC or SVC I have fluctuations in speed. This one is really strange and I'm looking for solution. Sure will ask mechanical to disassemble it again. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Slayer90
Slayer90
Cadet

Posted: ‎2025-02-17 12:46 AM

In response to Denys
0 Likes
0
1799
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 12:46 AM

ok thanks for the information. However, I have current fluctuations, not speed. in my case I solved the problem by inserting a value increased by approximately 10% of the rated motor current instead of the motor current write on motor nameplate. Most likely the engine has some problem or the nameplate on it has some incorrect value. I had also tried with a temporary cable for the encoder but nothing had changed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Ramazan_Tuncer
Ramazan_Tuncer
Cadet

Posted: ‎2025-04-04 05:02 AM

0 Likes
0
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-04 05:02 AM

Dear all,

 

I have the same problem with closed loop control in an extruder application with no load. Only the gearbox connected to the motor at the moment. 75 Hz is the nominal speed of the motor and these fluctuations starts at 60 Hz. I tried to optimize the speed performance with gain parameters SPG, SIT and even tried with high performance speed loop control.

My observation is that these fluctuations start when the actual torque comes around 0%.

 

We will couple the load soon and I don't know if we will have the same problem at load.

Any suggestion is welcome.

 

Thanks in advance.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

SESA153041
Crewman SESA153041 Crewman
Crewman

Posted: ‎2025-04-07 12:29 AM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-07 12:29 AM

Hello,

 

We have a similar experience on a 800kW Archimedes screw application driven by an ATV9B0C80Q6X1 + asynchronous WEG motor in closed loop. 

 

If we monitor SRFR (blue curve) we notice speed oscilations of about 0,3Hz around 50Hz.

 

Drivebord Pomp 1_310325_Nood_Pompen_5m3 (Final).png

We tried to solve this issue by changing SPG, SIT, SFC, CRB, CRTF, FFH,... but none of these parameters seem to have an influence.

 

Feel free to share your comments.

 

Kind regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore