ATV6000 Cell Bypass Voltage availability
  • Industrial Automation
  • Solutions for Motor Management
  • ATV6000 Cell Bypass Voltage availability
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
15
Back to Solutions for Motor Management
PrashantCPatange
PrashantCPatange Cadet
Cadet
Posted: ‎2025-07-16 10:16 PM
519
In case of ATV6000, during cell bypass operation, what will be the % voltage available at the output of drive with various nos. of cell bypass condition? E.g with 1 cell bypass, 2 cell bypass, 3 cell bypass for 6.6kV & 11kV drives.
Also what will be the situation in ATV6100 for the same. (Considering only single phase cell bypass with Neutral shift design)
  • Medium Voltage AC Drives
PriscilaCunha22
Lieutenant JG
Posted: ‎2025-07-18 01:37 AM
507
Hello @PrashantCPatange
For ATV6000, we bypass all 3 phase.
For 6,6kV we have 5 power cells per phase and 11kV we have 9 power cell per phase.
Each power cell is 720V, so you can calculate the phase-neutral voltage and phase-to phase voltage.
For 6,6kV - with 1 bypass the output voltage is 80%.
For 11kV - with 1 bypass the output voltage is 88,9%.
For ATV6100, we have the "Angle Adapted Bypass" and we bypass only 1 power cell, not the 3 phase.
For 6,6kV - with 1 bypass the output voltage is 90%.
For 11kV - with 1 bypass the output voltage is 94,4%.
PriscilaCunha22
Lieutenant JG
508
TonyStark
TonyStark
Cadet
Posted: ‎2025-10-13 05:21 AM
In response to PriscilaCunha22
Hello
I wanted to confirm something of vfd atv6100
- In case of n+1 cell config, redundant cell is active or inactive in normal mode?
- How many pulse of isolation transformer in n+1 cell config? 30 pulse or 36 pulse?
Hope to hear from you soon!
Eng.Ehab
Eng.Ehab
Cadet
Posted: ‎2025-11-25 04:44 AM
Hello
I wanted to understood something of VFD, how bypass work at fault Power cell (will shorted  by new of insulated-gate bipolar transistor or same damaged insulated-gate bipolar transistor) and
can be change automatic at N+1 (at the same line)