ATV 320 Braking resistor

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • ATV 320 Braking resistor
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
48
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
12
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
11
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Solutions for Motor Management
Anonymous user
Not applicable

Posted: ‎2021-02-04 12:33 PM . Last Modified: ‎2022-12-02 04:10 AM

1 Like
7
5067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-04 12:33 PM . Last Modified: ‎2022-12-02 04:10 AM

ATV 320 Braking resistor

I have an ATV320...C frequency convertor of Schneider. I want to connect a braking resistor. I have to use PB an P0.

 

The question is whether the bridge between P0 and PA / + must remain in order to switch on the brake resistor?
I suppose so. There is no direct information about this bridge in the manuals.
There is a notch at the position of the terminal P0 that you can break off to connect the wire in P0. I wonder its function?
Don't touch the notch and so connect to PA / + I suppose? Or is this wrong.

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Rodrigo_Garcia
Commander Rodrigo_Garcia Commander
Commander

Posted: ‎2021-02-10 07:54 AM

0 Likes
0
5040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-10 07:54 AM

Hello @Eric_Coudurier , Could you support on this? Thanks!

Rodrigo G. 


Industrial Automation Community manager

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-02-23 11:00 PM . Last Modified: ‎2021-02-24 10:28 PM

0 Likes
4
4998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-23 11:00 PM . Last Modified: ‎2021-02-24 10:28 PM

The ATV320 has 2 model types.
On the ATV320...B drives, the braking resistor should connect between terminals PB and PBe.
On the ATV320...C drives, the braking resistor should connect between terminals PB and PO.

Also, verify that parameter brA (Deceleration Ramp Adaptation) is set to NO.  Factory default for brA parameter is Yes.  The drive will not use the braking resistor if brA is set to Yes.  The brA parameter can be found at the following menu location:  COnF - FULL - FUn - rPt - brA - UPSers

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-12-28 03:51 AM

In response to Anonymous user
0 Likes
3
4508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-28 03:51 AM

The ATV320 has 2 model sorts.
On the ATV320...B drives, the slowing down resistor ought to associate between terminals PB and PBe.
On the ATV320...C drives, the slowing down resistor ought to associate between terminals PB and PO.

Likewise, check that boundary brA (Deceleration Ramp Adaptation) is set to NO. Manufacturing plant default for brA boundary is Yes. The drive won't utilize the slowing down resistor on the off chance that brA is set to Yes. The brA boundary can be found at the accompanying menu area: COnF - FULL - FUn - rPt - brA-MyLowes

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

wayneoo
wayneoo
Cadet

Posted: ‎2022-04-05 10:14 PM

In response to Anonymous user
0 Likes
2
4419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-05 10:14 PM

Most drives incorporate the Dynamic Braking semiconductor so the outside slowing down resistor will be wired between the PA and PB terminals.
There will either be a jumper or a DC stifle associated among PA and PO. It is essential to ensure this isn't taken out on the grounds that the drive won't work without it.
For the ATV12 and for high strength drives (ATV61, ATV71) an inside semiconductor is excluded and would need to be added to the drive as an outside module.
For the ATV320 series, there are two sorts of drives. The Bookcase (Part number finishes with B) and the Compact (Part number closures with C). For the B form, interface the resistor between terminals PBe and PB. For the C rendition, associate the resistor among PO and PB.
The ATV600 group of drives can't be associated with a slowing down resistor. Furthermore, there is no PB terminal.
Counsel your particular drives Installation manual for subtleties.Upsers

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

andrewwww
andrewwww
Cadet

Posted: ‎2022-04-20 10:34 PM

In response to wayneoo
0 Likes
1
4258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-20 10:34 PM


@wayneoo wrote:

Most drives incorporate the Dynamic Braking semiconductor so the outside slowing down resistor will be wired between the PA and PB terminals.
There will either be a jumper or a DC stifle associated among PA and PO. It is essential to ensure this isn't taken out on the grounds that the drive won't work without it.
For the ATV12 and for high strength drives (ATV61, ATV71) an inside semiconductor is excluded and would need to be added to the drive as an outside module.
For the ATV320 series, there are two sorts of drives. The Bookcase (Part number finishes with B) and the Compact (Part number closures with C). For the B form, interface the resistor between terminals PBe and PB. For the C rendition, associate the resistor among PO and PB.
The ATV600 group of drives can't be associated with a slowing down resistor. Furthermore, there is no PB terminal.
Counsel your particular drives Installation manual for subtleties.Upsers


thanks for the help us

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2022-04-22 06:09 AM

In response to andrewwww
0 Likes
0
4222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-22 06:09 AM

As a complement about ATV600 remark above. Let me explain why the ATV600 does not have possibility to use a braking resistor : just because the targeted applications for this family is "Process" mainly on pumping applications and also some on fans.

For Fans, sometime, it could be necessary to use an external braking resistor, when a stopping time is required and specified. In this situation, it is advised to use ATV900 with the possibility to connect an external braking transistor.

Hope this will help... 

Bruno Jacqz, Drives training leader
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Roger_Conlin
Roger_Conlin
Cadet

Posted: ‎2022-04-22 06:19 AM

1 Like
0
4217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-22 06:19 AM

Yes, the jumper between PO and PA/+. Only remove the jumper when installing an external DC choke.  

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of