I have a few Interval Trend Logs on an AS in a specific folder. This AS is attached to an ES.
"03/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs"
In a SmartConnector, I would like to get Interval Trend Logs using EwsClient.ExtractHistoryItemIds or EwsClient.ExtractHistoryItems.
When I call using these parameters, it does not work.
itemIds = c.ExtractHistoryItemIds(false, new List<string> { "03/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5); items = c.ExtractHistoryItems(false, new List<string> { "03/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5);
But when I call the same method using the true parameter, it returns but takes a while to return.
itemIds = c.ExtractHistoryItemIds(true, new List<string> { "03/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5); items = c.ExtractHistoryItems(true, new List<string> { "03/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5);
The EwsClient version is 2.2.108.0
I assumed that if the path to the logs is known, passing false should work. Is there some setting on the AS that should be set or some other parameter I am missing?
Thanks in advance!!
Link copied. Please paste this link to share this article on your social media post.
Hi Maneesh,
I think this isn't working because when it is set to False it is expecting a list of Container Items Ids, but from what I can see, you havent passed in any ContainerItem Ids, but actually HistoryItem Ids.
itemIds = c.ExtractHistoryItemIds(false, new List<string> { "03/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5);
items = c.ExtractHistoryItems(false, new List<string> { "03/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5);
should probably be changed to:
itemIds = c.ExtractHistoryItemIds(false, new List<string> { "00/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5);
items = c.ExtractHistoryItems(false, new List<string> { "00/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5);
Notice 03 has been changed to 00 in the prefix of your Container Item IDs.
Below are what the prefixes in the SBO EWS Ids mean:
00 - Container Item
01 - Value Item
11 - Value item, that is a property of another Value Item
02 - Alarm Item
03 - History Item
-Jeff
Link copied. Please paste this link to share this article on your social media post.
Hi Maneesh,
I think this isn't working because when it is set to False it is expecting a list of Container Items Ids, but from what I can see, you havent passed in any ContainerItem Ids, but actually HistoryItem Ids.
itemIds = c.ExtractHistoryItemIds(false, new List<string> { "03/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5);
items = c.ExtractHistoryItems(false, new List<string> { "03/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5);
should probably be changed to:
itemIds = c.ExtractHistoryItemIds(false, new List<string> { "00/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5);
items = c.ExtractHistoryItems(false, new List<string> { "00/Server 1/Servers/DFW18_S220_DCIM04/TrendLogs" }, 5);
Notice 03 has been changed to 00 in the prefix of your Container Item IDs.
Below are what the prefixes in the SBO EWS Ids mean:
00 - Container Item
01 - Value Item
11 - Value item, that is a property of another Value Item
02 - Alarm Item
03 - History Item
-Jeff
Link copied. Please paste this link to share this article on your social media post.
I see. That explains it. Thanks!