Unable to add Processor assembly after upgrading from V2.4.10 to V2.4.17 or later versions.

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Unable to add Processor assembly after upgrading from V2.4.10 to V2.4.17 or later versions.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
sesa145614_brid
Ensign sesa145614_brid Ensign
Ensign

Posted: ‎2020-04-10 06:07 PM

0 Likes
2
998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-10 06:07 PM

Unable to add Processor assembly after upgrading from V2.4.10 to V2.4.17 or later versions.

I have processor assembly which worked fine on V2.4.10 but can not be selected after upgrading SmartConnector to V2.4.17. (I rebuilt the assembly with V2.4.17.)

 

Is there any code changes needed between these two versions?

V2.4.17.jpg 

 

V2.4.10.jpgI

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2020-04-13 12:18 PM . Last Modified: ‎2020-04-13 12:31 PM

0 Likes
1
994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-13 12:18 PM

Hello!

 

Prior to 2.4.17 Smart Connector was built as a 64-bit process, but was only running as a 32-bit process due to a wrong build setting. This was causing significant performance issues in extensions that made heavy use of the in-memory cache. In 2.4.17 this setting was fixed, and now the Smart Connector service runs as a 64-bit service by default. This had the unintended consequence of breaking extensions that had a dependency on a 32-bit only .dll, which would be my guess as to why this is no longer working for you.

 

If this is the case, or if you are not sure; at the download center on www.smartconnectorserver.com we have now included a 32-bit runtime for the Smart Connector service .exe. Download this file for the version of Smart Connector you have installed on your machine, and replace the Mongoose.Service.exe file in your install directory with the one from the below link. There is also a readme in the same directory that explains what this file is for, and how to use it.

 

https://www.smartconnectorserver.com/DownloadCenter/Contents/mongoose/v2.4/32-bit%20Only

 

Let me know if this doesn't work or you have additional questions

 

Best Regards,

 

-Jeff

See Answer In Context

Reply
Replies 2
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2020-04-13 12:18 PM . Last Modified: ‎2020-04-13 12:31 PM

0 Likes
1
995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-13 12:18 PM

Hello!

 

Prior to 2.4.17 Smart Connector was built as a 64-bit process, but was only running as a 32-bit process due to a wrong build setting. This was causing significant performance issues in extensions that made heavy use of the in-memory cache. In 2.4.17 this setting was fixed, and now the Smart Connector service runs as a 64-bit service by default. This had the unintended consequence of breaking extensions that had a dependency on a 32-bit only .dll, which would be my guess as to why this is no longer working for you.

 

If this is the case, or if you are not sure; at the download center on www.smartconnectorserver.com we have now included a 32-bit runtime for the Smart Connector service .exe. Download this file for the version of Smart Connector you have installed on your machine, and replace the Mongoose.Service.exe file in your install directory with the one from the below link. There is also a readme in the same directory that explains what this file is for, and how to use it.

 

https://www.smartconnectorserver.com/DownloadCenter/Contents/mongoose/v2.4/32-bit%20Only

 

Let me know if this doesn't work or you have additional questions

 

Best Regards,

 

-Jeff

Reply
sesa145614_brid
Ensign sesa145614_brid Ensign
Ensign

Posted: ‎2020-04-13 06:35 PM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-13 06:35 PM

Hi Jeff,

 

Yes, this is the solution!

 

I used the x86 version of Mongoose.Service.exe and it showed the selection of the Update Processor. I also built the assembly as x64 and it worked fine with the relased verion.

 

Thank you!

 

Juh

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore