Swagger Username and Password Incorrect

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Swagger Username and Password Incorrect
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
petri_greenwave
Lt. Commander | EcoXpert Master petri_greenwave Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2017-04-08 04:25 AM

0 Likes
6
3409
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-08 04:25 AM

Swagger Username and Password Incorrect

Hi All,

I have started looking into the SmartConnector application as one of our major clients would like to pull Values and Trends from their Automation servers and Enterprise servers onto their own Webpage using the EWS RESTful Gateway.

I have setup everything according to the documents however I am getting stuck when trying to use Swagger to do some testing.

When I click on the Swagger link http://127.0.0.1:8083/swagger/docs/v1 as an example on my Endpoint it takes me to the page where I supposedly can do some test queries. However, It asks for a username and password which for the life of me I can't figure out. According to the EWS RESTfull gateway document I am supposed to, using a soapewsrestprovider, use the EWS user on the referenced server.

Now, since there is no specific user for EWS on the automation server/Enterprise server, I would assume using the admin account should grant me access. Unfortunately it keeps saying incorrect username or password.

Which username /password should I be using to authenticate swagger so I can test my SmartConnector Endpoint?

Tags (2)
  • Tags:
  • smartconnector
  • swagger
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2017-04-10 06:54 AM

0 Likes
2
3299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-10 06:54 AM

Petri,

I had another thought as well.  I noticed that you configured the REST endpoint using the default port of 8083.  Did you happen to delete the other REST endpoint that is added as sample data?  That happens to also use port 8083.  If you didn't delete it, you might be seeing a weird issue where Swagger thinks it's connecting to your REST endpoint for SBO but it's actually not.  You would see that on the endpoint configurations page where only one of the endpoints would be actually running.

See Answer In Context

Reply
Replies 6
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2017-04-08 10:02 AM

1 Like
0
3299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-08 10:02 AM

What you stated is correct; to connect to SBO, you need to use the SoapEwsRestProvider and valid credentials from the ES or AS you stated.

What value did you enter into the Endpoint Configuration's Http Configuration Server Address field?  It needs to be the address for the EWS endpoint and should look like this:http://localhost:8081/EcoStruxure/DataExchange (change localhost and the port as needed).

Reply
petri_greenwave
Lt. Commander | EcoXpert Master petri_greenwave Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2017-04-08 12:58 PM

0 Likes
4
3299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-08 12:58 PM

Hi Mark,

Thanks for the response.

If I understand correctly, the server address should be the Automation Server or Enterprise Server you are using's IP.

For instance, if I want to pull trend logs or alarm events into a client's webpage , using smartconnect, I would enter the server I am connecting to, or consuming from,'s address in the Server Address field.

So for the 2 examples I tried (first AS, then ES) I had http://>exampleASIP</EcoStruxure/DataExchange and http://>exampleESIP</EcoStruxure/DataExchange as the server addresses. I tried http and https in both cases after I changed the "Enforce Secure Communication" setting to enable as well.

I used the AS, and ES passwords in swagger but it kept returning "The Username or Password were incorrect."

I am sure I'm missing something and would appreciate it if you could tell me what

Reply
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2017-04-10 06:50 AM

0 Likes
3
3299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-10 06:50 AM

Hi Petri,

Is your admin user on the default SBO domain? EWS users must be on the default domain of SBO.

You don't need to enforce secure communications for this to work (but of course the added security is nice ).

In any case, if you could provide us with the following information, we could more easily help you debug this issue:

- What version of SBO and SmartConnector are you using?

- In the SmartConnector Logging filters page, could you turn on Ews Consume, and Rest Serve and in the Settings page set the logging level to Debug. Run your test again, and send us the SmartConnector log (c:\ProgramData\SmartConnector\Logs) after you try and authenticate.

- If you could get some Fiddler and/or Wireshark captures of the handshake that could help as well.

Regards,

-Jeff

Reply
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2017-04-10 06:54 AM

0 Likes
2
3300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-10 06:54 AM

Petri,

I had another thought as well.  I noticed that you configured the REST endpoint using the default port of 8083.  Did you happen to delete the other REST endpoint that is added as sample data?  That happens to also use port 8083.  If you didn't delete it, you might be seeing a weird issue where Swagger thinks it's connecting to your REST endpoint for SBO but it's actually not.  You would see that on the endpoint configurations page where only one of the endpoints would be actually running.

Reply
petri_greenwave
Lt. Commander | EcoXpert Master petri_greenwave Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2017-04-11 06:24 AM

0 Likes
1
3299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-11 06:24 AM

Hi Mark,

Thank you, that did the trick. I deleted the original endpoint and it took the password first time.

Now... to resume testing

Reply
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2017-04-11 06:26 AM

0 Likes
0
3299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-11 06:26 AM

Petri,

Glad it's working for you now.  If you have any other questions, don't hesitate to ask.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore