SmartConnector stopped sending data to EBO

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • SmartConnector stopped sending data to EBO
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
ardak
ardak Schneider Alumni (Retired)
34
sesa180908_brid
Commander sesa180908_brid Commander
34
mike_meirovitz
Commander mike_meirovitz
21
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SmartConnector Forum
Start a Topic
AQ
Lieutenant JG AQ
Lieutenant JG

Posted: ‎2021-09-01 04:09 AM

0 Likes
3
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-01 04:09 AM

SmartConnector stopped sending data to EBO

Good day,

 

I've noticed that SmartConnector stopped sending tags values to EBO.

I can host EWS objects, every tag in EWS server get sent to a proper interface in EBO.

But all tags have uncertain state, all of them are equal to 0.

Do you have any idea how to solve this issue?

 

Regards

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
jorge_initech_e
Lieutenant | EcoXpert Master jorge_initech_e Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2021-09-07 11:18 PM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-07 11:18 PM

I had a similar issue with the smart connector i'm currently developing. In my case, i was using Sql Server Express as database, that has a size limitation. I've noticed that each time a value is sent to the client it also gets stored as "NotificationItem" in a database table, to the point, that if you have a lot of transactions, it can reach the database size limit and stop sending values to the client (EBO).

The only way i've found to solve it, is empty the notification tables by hand  on the database and clear the log, that way it worked again for me.

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-09-13 02:31 AM

0 Likes
1
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-13 02:31 AM

Hi, it's hard to say without knowing exactly what you're doing in your code, but Jorge's explanation is one possibility. Check your database if it's full.

 

@jorge_initech_e If this is happening to you, I recommend using the EwsServerCleanupProcessor in the Smartconnector.Utilities package. 

 

When configured and scheduled this processor cleans up notification and subscription items which are no longer needed on your adapter, therefore also cleaning up the database. This way you don't have to do it manually in your code.

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply
AQ
Lieutenant JG AQ
Lieutenant JG

Posted: ‎2021-09-17 07:10 AM

0 Likes
0
1123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-17 07:10 AM

Thanks for replies. It wasn't related with SQL database.

Mongoose.service.exe config was somehow faulty, contained no informations about logging data. Adding few lines allowed to renew communication. 

Tags (1)
  • Tags:
  • english
Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore